Additional sub panel

Discussion in 'Electrical Forum discussion & Blog' started by tnbuilder, Aug 8, 2009.

  1. tnbuilder

    tnbuilder New Member

    Joined:
    Aug 8, 2009
    My house has a 200 amp service with an exterior cutoff panel adjacent to the meter base. Breaker 1 is 70 amps for exterior AC/Heating circuits. Breaker 2 is 90 amps and controls the interior load center/subpanel.

    According to the 2002 NEC load calc, I currently require 80 amps available from the existing 90 being fed to the interior load center.

    I got an electrical permit (based on 2002 NEC), and am starting to wire an addition which includes master bedroom, bathroom, laundry, kitchen expansion. Can I add a third breaker to the exterior cutoff panel/load center and run a new SER, 4 wire cable cable to a new subpanel? The addition needs approx 40 amps. Should I use #4 copper for a 50' run through a crawl space?
     
  2. Speedy Petey

    Speedy Petey Licensed Electrical Contractor

    Joined:
    Jun 16, 2007
    Occupation:
    Licensed Electrical Contractor
    Location:
    NY State, USA
    If the addition needs 40A @ 240v then you can run #6 cable from a 50 or 60A breaker. You can also run the #4cu to a panel off a 100 or 90A breaker.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
Similar Threads: Additional panel
Forum Title Date
Electrical Forum discussion & Blog using copper waterlines under slab for additional ground ? Mar 25, 2013
Electrical Forum discussion & Blog Sub Panel Install Question Thursday at 8:30 PM
Electrical Forum discussion & Blog Service Upgrade & Sub Panel Installation Apr 17, 2015
Electrical Forum discussion & Blog Sub Panel install Mar 4, 2015
Electrical Forum discussion & Blog Does a sub panel in attached space need a main breaker? Feb 20, 2015

Share This Page