Valveman is right, as always. We don't normally check rotation of 3 phase submersible motors before installation. You have a 50% chance of getting it right. A submersible pump running in reverse rotation will pump about 60% of normal. You start it up, check flow & pressure. Then shut it off, reverse two leads and check it again. It's very obvious which is the correct rotation. On wells with a deep static water level, often times the pump won't pump water to the surface in reverse.
On larger 3 phase motors, the next step it to balance the loads on each leg as much as possible. You check the amperage on each leg, then move each wire one position. Amperage is checked again. The wire are moved again and amperage is checked again. One of the three setups will have the least imbalance between legs. This is how you want to leave the pump wired. Moving all three wires one position will keep the motor rotation the same. Swapping any two wires changes the direction of rotation.
On lineshaft turbines, the motor is not connected to the line shaft, or "clutched up", until the rotation is checked. If the motor were to be run in reverse, it would unscrew the lineshaft couplings down hole. I have seen lineshaft come up thru the motor bonnet, then thru the pump house roof when the motor was wired incorrectly.