80% humidity in Crawlspace
Discussion in 'Plumbing Forum, Professional & DIY Advice' started by ALLEN18, Aug 3, 2012.
  1. ALLEN18
    ALLEN18 New Member
    Aug 3, 2012
    Chicago
    I moved into a new house with a crawl, about 300 Square feet. It was built in 1956, it's in Chicago, IL. Currently has a Dirt Floor and 2 vents that are open. I am running a dehumidifier which brings humidity down to 50% but once it stops running goes back up to 80%. I have not noticed any leaks but is it likely that the sewer line is cracked and the moisture is seeping up through the Dirt floor? If so, what is my next step?
  2. mikeplummer
    mikeplummer Plumber
    Mar 28, 2012
    Ontario, Canada
    you could have someone check the sewer line for damage, a service company with a sewer cam. likely moisture from the ground itself. put down vapour barrier...make sure its done properly....ie overlap and tape joints and seal it to the wall with acoustic sealant..
  4. ALLEN18
    ALLEN18 New Member
    Aug 3, 2012
    Chicago
    Ok getting the sewer lines checked out next week, $199 for rotting and sewer cam. Not sure if that is a good deal or not.
    What are your thoughts on pouring concrete in crawl?
  5. bpbailey
    bpbailey New Member
    Aug 13, 2012
    Champaign, IL
    install a vapor barrier
    What is the humidity of the outside air? If you have a vented crawl space and a dirt floor, the humidity in the crawl space will probably be the same as the outside air. You mention that you are running a humidifier and this lowers the humidity until you turn it off. This makes sense because you also state that the crawl space is vented, which means outside air circulates through the crawl space. You are effectively dehumidifying the outside air. Whether you have a cracked sewer pipe has nothing to do with the humidity in the crawl space. One good option is to lay an appropriate vapor barrier over the dirt floor. This will make a huge difference. And, in addition, you can seal the crawl space and install rigid foam around the inside perimeter of the crawl space for insulation. Then install a dehumidifier appropriate for a crawl space such as a Sani-Dry system. That will take care of the problem.
    -Brian
  6. Dana
    Dana In the trades
    Jan 14, 2009
    01609
    In Chicago the subsoil temperatures are well below the average dewpoint of the outdoor air, so when that air enters the much cooler crawlspace it's relative humidity climbs through the roof.
    The primary source of the humidity is not a mystery- it's the outdoor air coming in the vents! The average outdoor dew point in Chicago is in the mid-60sF, and the deep subsoil temp is around 50F, so in the summer the crawlspace will run much cooler than the outdoor air, with heat being pulled into the soil. The air temp in the partially-vented crawl space may run 68-70F even when the outdoor air is in the 80s unless the ventilation rate is extremely high (not likely, with passive vents). With an outdoor dew-point of 65F, cooling the air to 70F yields a relative humidity of ~81%. When the outdoor dew points hit the 70s (which does happen in Chicago), the relative humidity is higher still.
    If it doesn't stink like sewage down there, only moldy/musty, it's highly unlikely that you have a contribution from your house drains, and the $199 inspection is a waste of money.
    If you're running a dehumidifier in there with the vents open you're using 3-10x as much power as you would if you seal up the vents, since with the vents open you're trying to dehumidify the whole great-outdoors. If you seal the vents (highly recommended in your climate, even if code requires that you make them operable to vent after a flood) it's also important to put down a ground vapor barrier sealed to the foundation walls to control both ground moisture & other soil gases.
    You can use 6-mil poly (10 mil is better), as a vapor barrier, lapping the seams between sheets by about a foot, and sealing the seams with duct-mastic (normally used for sealing heating/cooling ducts, available at box-stores). At the foundation walls run it up the wall by about a foot and hold it in place with furring through screwed to the foundation with Tapcons every few feet, sealing the edge with duct mastic. In most Chicagoland homes it would also be cost-effect from a heating & cooling cost point of view to insulate & seal over the foundation wall right up & over the foundation sill & band-joist with 2" of closed cell spray polyurethane (spraying over the vapor-retarder furring is OK), but that can be treated as a separate project. Even with the vents closed up, the air leakage into the crawl at the foundation sill & band joist is significant, and insulating over them with ccSPF makes it pretty air-tight.
    In general vented crawlspaces ADD more humidity than they remove in most US climates east of the high-plains east of the Rockies. Though it was required by code for decades, there is little science behind it, and it's inappropriate for climates with summertime humidity as high as Chicago.
    Pouring concrete in the crawl (even a non-structural 1-2" rat-slab) is a good idea. But down 3" of 1/2" screenings/pea-gravel, then a 10-mil vapor barrier, with the concrete on top of that. The gravel is a capillary break & drain, mitigating liquid water from ever coming up through the seams in the vapor barrier, and the concrete protects the vapor barrier. If you're planning to insulate the foundation walls, adding 1-2" of rigid EPS insulation under the slab between the gravel and vapor barrier is cost-effective in the long-term.
Similar Threads: humidity Crawlspace
Plumbing Forum, Professional & DIY Advice Humidity streaks Oct 31, 2016
Plumbing Forum, Professional & DIY Advice crawl space humidity Sep 29, 2013
Plumbing Forum, Professional & DIY Advice Drain Line Repair in Crawlspace - am I being over quoted? Dec 14, 2016
Plumbing Forum, Professional & DIY Advice Waterproof enclosure for PEX manifold in attic crawlspace? Nov 17, 2014
Plumbing Forum, Professional & DIY Advice Is this cost estimate Reasonable? Repipe waste in crawlspace Jul 10, 2012
