2"main stack vent, big enough??

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by rheagle1, Mar 20, 2005.

  1. rheagle1

    rheagle1 New Member

    Joined:
    Mar 10, 2005
    Currently we have a 4"cast iron main stack/drain pipe. We are putting in a new bathroom, and going to be taking out the old main vent. We are wanting to just use a 2" main vent in the wall since the current walls are only 2x4. All that would be going off this vent would be the toilet, sink, and tub then going to the sewer line. We will be tapping back into this 4" pipe in the attic. Eventually we will be redoing the kitchen and it will have it's own 2" vent going to the sewer and attic. Will this work, or cause problems. Thanks much.
     
  2. Master Plumber Mark

    Master Plumber Mark Master Plumber

    Joined:
    Feb 6, 2005
    Occupation:
    Sensitivity trainer...to be caring and loving to a
    Location:
    indianapolis indiana - land of the free, home of
    depends on where you live

    I am down with the flu today so I have ben posting on here like a mad man.
    Better than just sitting in bed.

    ------------------------------------------------------------------------
    In indiana, all you need is one 1 1/2 vent going out of the roof to do the whole home....even a 3 -5 bathroom home!!

    they claim its all just air, and the system works the same wether its 1/1/2 or 3 inch

    Its good to have a couple of vents out the roof if it can be done, but its not really necessary



    just call a local plumber and get a free estimate.
     
    Last edited: Mar 20, 2005
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    If this were in UPC plumbing code country, you would need a composite 4" venting the home, that could be done by combining four 2" vents.

    You will notice that many homes have several pipes, (vents) on the roof.
    Working with a 3" waste line out of the home, you will often see two 2" vents and one 1.5" vent.
    Will the plumbing work with the 2" vent? Yes.
    When I'm plumbing, I count up the vents leaving the roof, the inpector will too. Ask the inspector first, what he will allow before committing too much time to this.
    If I plumb, I do it to the code book, then I don't have to worry. It's much quicker to do it right, then it is to try to convince someone against it.
    Tub 2.0 fixture units
    Lav, 1.0 fixture units
    Toilet, 3.0 fixture units
    Total, 6.0 fixture units

    A 2" pipe will handle 24 fixture units, that's like four bathroom groups.
    When I'm plumbing condo's and apartments, I may have eight or ten four-story groups that look somewhat like this but taller.

    http://www.iapmo.org/common/ROP2004/upc04rop/preprint/ch7.pdf


    [​IMG]
     
    Last edited: Mar 20, 2005
  5. rheagle1

    rheagle1 New Member

    Joined:
    Mar 10, 2005
    Thanks! I think we'll end up doing the 3" vent. From the calls I made sounds like that's the code. Guess I better do it then :D
     
Similar Threads: 2main stack
Forum Title Date
Plumbing Forum, Professional & DIY Advice Condo Shared Vent Stack Question Jul 10, 2015
Plumbing Forum, Professional & DIY Advice Need for vent stack? May 29, 2015
Plumbing Forum, Professional & DIY Advice DIY Question: Replace Partial Cast Iron Sewer Stack May 19, 2015
Plumbing Forum, Professional & DIY Advice DIY question about getting angles right from stack to closet flange. Apr 6, 2015
Plumbing Forum, Professional & DIY Advice Main stack vent size ? Apr 4, 2015

Share This Page