Can I run one 2 inch water stack for a washer on first floor and a washer on the second floor ??? Thanks kevin
. Thank u sounds greatA WM has a fixture limit of 3, and a 2" pipe can support up to 16, so, if I'm reading the tables properly, you can put two WM on a 2" pipe.
That is correct, at least between the two, you need a second pipe to act as the vent from the first floor. You can join it with the vent from the second floor, so you only need one to go out the roof, or potentially, join it into an existing one to prevent putting a new hole in the roof. Note, any horizontal sections of the vent need slope, just like any drain, since they could have precipitation or condensation and that must drain, keeping the vent open.Ok thank so I can not drain the 2 nd floor washing into the vent of 1 st floor washer if I understand that correctly
Floodsafe hoses have bad reports, but they were not being discussed on this thread.I think I read some not so good reports on the Floodsafe hoses...may be wrong...do a search and see.