12/2 with ground but outlet ungrounded

Users who are viewing this thread

draven8795

New Member
Messages
37
Reaction score
0
Points
0
Location
Wisconsin
So my stove electronics died twice and finally tracked it down to the outlet not having a ground.

I opened up the outlet and i do have 12/2 with a ground but the ground screw on the actually outlet is not connected.

Can I simply connect a piece of copper wire from the outlet ground screw to the ground on the existing 12/2 with ground?

I have done this and checked with one of those outlet testers and it says its grounded but I figured I'd ask here before I plug the stove in.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
So my stove electronics died twice and finally tracked it down to the outlet not having a ground.

I opened up the outlet and i do have 12/2 with a ground but the ground screw on the actually outlet is not connected.

Can I simply connect a piece of copper wire from the outlet ground screw to the ground on the existing 12/2 with ground?

I have done this and checked with one of those outlet testers and it says its grounded but I figured I'd ask here before I plug the stove in.

The death of the electronics on you stove has nothing to do with the missing equipment grounding conductors unless there was a fault in the electronics in which case the equipment grounding would have only served to clear the fault and the electronics would have been lost any way.

If the cable has a ground why not just replace the receptacle with the proper three wire receptacle?

Am I missing something here?
 

draven8795

New Member
Messages
37
Reaction score
0
Points
0
Location
Wisconsin
The death of the electronics on you stove has nothing to do with the missing equipment grounding conductors unless there was a fault in the electronics in which case the equipment grounding would have only served to clear the fault and the electronics would have been lost any way.

If the cable has a ground why not just replace the receptacle with the proper three wire receptacle?

Am I missing something here?

Oh i think i mis-worded above. I have a 3 prong outlet already on the wall. However the actual three prong outlet does not have a ground wire connected to its ground screw. Whoever wired the house neglected to wire the ground wire to the outlet ground screw.

Today I connected a piece of copper wire from the outlet ground screw to the ground on the 12/2. This should now be a grounded outlet correct and my stove should now be grounded?

Am I thinking incorrectly that my stove would have died with or without the ground wire hooked up correctly?
 
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Explain what the word stove means.

Is this a gas cooking range?

Is this a gas stove for heat?

Is this a wood stove with a blower fan?

What kind of stove is this?

The equipment grounding conductor is installed in the event there is a fault to ground it will open the overcurrent device.
 

draven8795

New Member
Messages
37
Reaction score
0
Points
0
Location
Wisconsin
Explain what the word stove means.

Is this a gas cooking range?

Is this a gas stove for heat?

Is this a wood stove with a blower fan?

What kind of stove is this?

The equipment grounding conductor is installed in the event there is a fault to ground it will open the overcurrent device.

Its a gas cooking range.

Basically I just need to know if by connecting a new ground wire from the 12/2 wire to the three prong outlet. Am I grounded? My outlet tester says I am i just want some confirmation.

If a surge occurred without this ground connected could it have wrecked the electronic equipment for controlling the oven.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Its a gas cooking range.

Basically I just need to know if by connecting a new ground wire from the 12/2 wire to the three prong outlet. Am I grounded? My outlet tester says I am i just want some confirmation.

If a surge occurred without this ground connected could it have wrecked the electronic equipment for controlling the oven.


Without seeing the installation no one can say if it is correct or not. No the equipment grounding will not protect from surges.

If the electronics on the gas range was lost due to a power surge then more electronics throughout the house would have been lost.
 

Giles

Retired tool & Die and Mechanic
Messages
110
Reaction score
0
Points
16
Location
N.W. Alabama--Florence--
Explain what the word stove means.

Is this a gas cooking range?

Is this a gas stove for heat?

Is this a wood stove with a blower fan?

What kind of stove is this?

The equipment grounding conductor is installed in the event there is a fault to ground it will open the overcurrent device.
Would there be a different wireing procedure for the type stove involved?
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
Its a gas cooking range.

Basically I just need to know if by connecting a new ground wire from the 12/2 wire to the three prong outlet. Am I grounded? My outlet tester says I am i just want some confirmation.

If a surge occurred without this ground connected could it have wrecked the electronic equipment for controlling the oven.

You are at the outlet. If it's a metal box, you also need to ground the box.

But, like Mike said, that's not what caused the stove electronics to go; and if it had been connected, it would not have protected the electronics. These are separate issues.

It's still important, and a good thing you fixed it - the ground connection is there to protect you from getting fried.
 

draven8795

New Member
Messages
37
Reaction score
0
Points
0
Location
Wisconsin
You are at the outlet. If it's a metal box, you also need to ground the box.

But, like Mike said, that's not what caused the stove electronics to go; and if it had been connected, it would not have protected the electronics. These are separate issues.

It's still important, and a good thing you fixed it - the ground connection is there to protect you from getting fried.

Great well I guess I'll call in an electrician to see what might be the problem. I added a GFI outlet because that was what the maytag man said but when i switched the power on it just tripped and wouldnt reset. Guess I'll call an electrician to see what he can diagnois.

As for now i'm just using the regular grounded outlet i installed after the GFI. I'm confident its at least grounded.
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
Great well I guess I'll call in an electrician to see what might be the problem. I added a GFI outlet because that was what the maytag man said but when i switched the power on it just tripped and wouldnt reset. Guess I'll call an electrician to see what he can diagnois.

As for now i'm just using the regular grounded outlet i installed after the GFI. I'm confident its at least grounded.

If the GFI wouldn't reset with your stove plugged into it, I'd guess there's a ground fault somewhere in the stove. That means it's probably unsafe to use. Gotten any shocks off it?

Do you have a continuity tester? Check for continuity between the ground & neutral or hot.
 

draven8795

New Member
Messages
37
Reaction score
0
Points
0
Location
Wisconsin
If the GFI wouldn't reset with your stove plugged into it, I'd guess there's a ground fault somewhere in the stove. That means it's probably unsafe to use. Gotten any shocks off it?

Do you have a continuity tester? Check for continuity between the ground & neutral or hot.

I didn't even have anything plugged into the GFI and I double checked that I had the load and line correct so something else is going on with it.
 

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
Oh. Never mind, then.

...You got a receptacle tester?

GFCI_Receptacle_Tester.jpg


It might've been a faulty GFI, but that's pretty rare. So there might be something else weird going on.

Reversed polarity, for example, would screw up the electronics on a stove, and maybe kill a GFI.
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
It is good for *safety* to have the stove plugged into a properly wired and grounded receptacle.

So far as a ground being there and this protecting the stove electronics from "voltage surges", this is possible, but unlikely. The stove manufacturer would need to incorporate surge protection devices into the stove electronics. These parts would cost $1 more and manufacturers are cheap, so they don't tend to install these things. Also their sales of new stoves and repair revenues would go down if they made the stoves to last longer!

With that said, it is a good idea to get surge protector power strips or surge protector outlets for each location where something electronic is plugged in.

Also for things like a dryer, electric range, HVAC, etc. which uses 240 volts and for which surge protection power strips are not available, it is a good idea to install a "whole house surge protector" at the main electric panel.

I have had a whole house surge protector and surge protecting power strips at each electronics gizmo outlet for about 10 years and have never had any problems with my electronic things. And I live in a rural area where the power frequently goes out (can create surges).
 

draven8795

New Member
Messages
37
Reaction score
0
Points
0
Location
Wisconsin
It is good for *safety* to have the stove plugged into a properly wired and grounded receptacle.

So far as a ground being there and this protecting the stove electronics from "voltage surges", this is possible, but unlikely. The stove manufacturer would need to incorporate surge protection devices into the stove electronics. These parts would cost $1 more and manufacturers are cheap, so they don't tend to install these things. Also their sales of new stoves and repair revenues would go down if they made the stoves to last longer!

With that said, it is a good idea to get surge protector power strips or surge protector outlets for each location where something electronic is plugged in.

Also for things like a dryer, electric range, HVAC, etc. which uses 240 volts and for which surge protection power strips are not available, it is a good idea to install a "whole house surge protector" at the main electric panel.

I have had a whole house surge protector and surge protecting power strips at each electronics gizmo outlet for about 10 years and have never had any problems with my electronic things. And I live in a rural area where the power frequently goes out (can create surges).

I wouldn't say I'm rural but on the outer skirts of a town. I had a surge protector plugged in but without the ground it sounded from my research that the surge protector wouldn't do anything. I'm going to call an electrician to come take a look and see if he can figure out anything. I found the part that keeps frying online and its a 147 bucks. Depending on what the electrician has to say i'll probably wind up buying the damn extended warranty for this stove as its 137 bucks for 4 years.
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
So my stove electronics died twice ...........

Have you electrician check and see if you have a multiwire branch circuit supplying the range. I have seen some equipment failures due to an open neutral.

You can check this yourself if you are comfortable looking in the panel. If there are any red wires on the breakers, you will probably have MWBC's.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks