    As long as the main panel has a 100a main breaker, there's nothing to prevent you from installing another 100a breaker for another panel.
    My question would be: Is the main panel already supplying another panel somewhere else? If so, you may run into problems overloading the main by putting over 100 amps of load on it.
  3. jwelectric
    jwelectric Electrical Contractor/Instructor
    2,529
    North Carolina
    You can feed three or four 100 amp subpanels with that set up as long as the calculated load on the main does not exceed 100 amps
  4. Speedy Petey
    Speedy Petey Licensed Electrical Contractor
    988
    NY State, USA
    Typically a buss will have a maximum branch circuit breaker rating. Most are 100 or 125 amps.
  5. lahabra
    lahabra New Member
    50
    California
    No.
    When I’m done the main will only feed the new sub panel. Then I will connect 21 new circuits to the sub panel.
  6. Bill Arden
    Bill Arden Computer Programmer
    584
    MN, USA
    Nice main panel. :)
    I'm currently powering my 100A garage panel using a breaker coming out of my 100A house panel.
    The inspector was ok with it, but I know that I could trip the main if I turn everything on at the same time.
    Your case is better since the main panel only feeds the second panel and thus it is unlikely to overload the main panel.
    Edit: There is one thing you will have to deal with. The ground and neutral can only be tied together at the main and you then have to remove the ground screw in the second panel and run 4 wires to the main.
Similar Threads: 100A Main
Electrical Forum discussion & Blog Old house, 100A fusebox, should we replace w. breakers? Jan 12, 2012
Electrical Forum discussion & Blog wanting to add a 100A service to my garage Apr 4, 2008
Electrical Forum discussion & Blog 50 amp main breaker panel? No such animal Mar 26, 2014
Electrical Forum discussion & Blog What make/model box is this? Is it even a main or is it a sub panel? Jan 19, 2014
Electrical Forum discussion & Blog Wires from Main panael to Subpanel in two separate raceways? Aug 15, 2013