  1. Ron Read

    Chimney condensation after Utica TriFire boiler install

    Tonight I reconfigured the Reset controller with a curve more appropriate for the fin tube baseboard in my home. To steepen the curve to get the higher target temp while allowing a 35 degree differential to work while keeping boiler min at 140 I had to set the outdoor start at 80 degrees instead...
  2. Ron Read

    Chimney condensation after Utica TriFire boiler install

    I will try the higher min and max boiler temps on the reset and set the differential to manual and a number around 25 to start. Thank you for the input. This is the first boiler I have owned with an outdoor reset and I was not sure on settings but have been monitoring cycle times. The only...
  3. Ron Read

    Chimney condensation after Utica TriFire boiler install

    I had a Heating contractor install a Utica Trifire 4 section three pass boiler and Superstor 45 gallon DHW over the summer. The boiler AHRI rating is 79 MBH The Boiler vents into a tile lined 8X8 chimney that is on an exterior wall and is in perfect condition. Old Dunkirk boiler had a stack...