    18 year old Weil McLain boiler not working anymore?

    Thank you for all your info! The idea of insulating the pipes is greatly appreciated, since I did not think of that yet and it probably will make quite a difference. @Dana: Thank you also for pointing out to look for the manual. I am wondering if the manual you referenced is for the current...
  2. P

    18 year old Weil McLain boiler not working anymore?

    Thank you for your info so far. First thing I did was filling in more water to raise the pressure. The boiler now shows consistently a pressure of about 15 psi. I also adjusted the flow control valve as I mentioned before. The first issue I did have was that the radiators stayed completely hot...
  3. P

    18 year old Weil McLain boiler not working anymore?

    the cold water feed to the heating system is always turned off, while the heating system is in operation. However, I found that the flow control valve was in the open position and not set to actually prevent the gravity flow. I set it properly going that this could have done it. I did notice...
  4. P

    18 year old Weil McLain boiler not working anymore?

    I have a model CG 6-SPDN boiler built in 1994 for my hot water radiant heat (radiators) and will be using it also for radiant floor heating in an addition I am building. It has been running fine without any issues, however, a few weeks ago, it started acting differently. The boiler seems to...