  1. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    Solved! Seems my issue was combination pressure/water/air. Last night, when I was turning the coin valves on the air handler on the 2nd floor, I didn't get air or water...nothing came out. I knew my circ pump was working. My PSI was about 20. So what I did today was add water to the...
  2. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    To answer you..yes I have three corresponding valves I can turn off.
  3. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    I just took some pics with my camera, now they are too large for the site...ugh. I'll get more organized tomorrow and follow up. I appreciate everyones input and help. Scott
  4. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    pic of 2nd floor air handler Here's a few more, I hope they're helpful. the 2nd floor (You may notice the TACO says 3rd floor heat-that's what I call the 2nd floor) Anyway, the 2nd floor air handler is horizontal, above my wifes closet. this pic shows the unit. the valves: two are on...
  5. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    More pics coming soon. Inside the boiler there's a psi gauge. It shows a tad above 20psi
  6. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    I did the screwdriver to the ear thing and it does sound like it's spinning. Here's a few pics I'll take one of my airhandler upstairs and my piping by the boiler. Not sure if I mentioned this but I swapped what seem to be relays in the taco, but that did nothing. Thank you all.!
  7. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    Hi Thanks for replying. It probably is air as this is the same thing that happend last year. Also when I unscrew the valves in the 2nd floor air handler, nothing comes out. no water, no air. When I go to the basement airhandler and loosen the valves, water spurts out as expected. So my...
  8. MrBostn

    2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat

    Hi, Glad I found this forum. Perhaps someone can assist me. 2 zone system. Gas fired-forced hot water (not baseboards but air handlers-one in basement and one of 2nd floor) 3 circ pumps-and a taco controller. zone 1 works, the hot water system works-all 3 circ pumps turn on. Zone...