Search results

  1. sykotek

    Need Quick Answer, Inspector Coming Monday!

    I'm running a 30A line out from my garage (where main panel is) to a shed, 52 feet. I have spoken to the insoector earlier in the week and was told I can use UF-B direct bury cable at 24" which is what I am doing. I am running UF-B 10/2 with ground, just some sockets and lights, small...
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks