  1. sykotek

    Need Quick Answer, Inspector Coming Monday!

    I'll talk to the inspector then, if he lets me use the two insulated conductors in the 10/2 for the hots and the bare for neutral, then I'll just install a grounding rod out at the shed and run 220 to the panel. If not, then I'm not paying another $100 for a run of 10/3 for 220 to run some...
  2. sykotek

    Need Quick Answer, Inspector Coming Monday!

    Thank you! So I'll plan on putting a J box on the side of the house and conduit to the ground. The shed is raised off the ground and I plan on coming up under the wall sill plate vertically so am assuming I can just place conduit from ground level (or a few inches down) to the underside of...
  3. sykotek

    Need Quick Answer, Inspector Coming Monday!

    I'm running a 30A line out from my garage (where main panel is) to a shed, 52 feet. I have spoken to the insoector earlier in the week and was told I can use UF-B direct bury cable at 24" which is what I am doing. I am running UF-B 10/2 with ground, just some sockets and lights, small...