  1. NYCatskills

    Boiler over-pressurizing

    Drained the expansion tank last night and now it's got perfect pressure, between 12 and 16 just like it's supposed to. Thanks for the help.
  2. NYCatskills

    Boiler over-pressurizing

    John if I read you right I only think I'm draining the expansion tank when really it just stops putting out water because no air is coming in when opening the purge. Then I'll close the valve on the riser of the baseboard hot water to the house and open the drain just above it. The lateral...
  3. NYCatskills

    Boiler over-pressurizing

    House hot water is supplied by a coil running through the boiler. I should've mentioned that too, eliminated that possibility by turning off the cold water feed into that coil over night few days ago. Boiler still overpressurized. I notice that the pressure goes up when the hot water's being...
  4. NYCatskills

    Boiler over-pressurizing

    My boiler is over-pressurizing consistently for the past week when heating. If I lower the pressure by letting some water out from the relief valve in back of the boiler, the water fills to about 12 psi just like it's supposed to but once it starts heating up it gets up to 30 at which point it...