  1. C

    2 valves come on at once

    Fixed..... I ran a new low voltage line from the control box to the valve and everything works great. Must have been a cut in the wire somewhere causing the 2 wires to make a complete circuit all the time. Thanks for all the help and have a great summer.
  2. C

    2 valves come on at once

    There is no settings for program B but I did read that there can be problems where they hold settings in memory even though you do not see them. It says from rainbird to remove battery and fuse for a few minutes then put back and reprogram. I guess that will be my next attempt. I did play...
  3. C

    2 valves come on at once

    Update: I checked the power with a voltage meter in the valve box and verified both the red and blue have power when zone 1 or 2 are on. I then went back to the split and there was power on both wires so I went all the way back to the control box and both zone 1 and 2 have power at the same...
  4. C

    2 valves come on at once

    I think I know what might be causing this and will test this weekend. I think the red and blue wire may be touching each other somewhere between the controller and valve box causing it to complete the circuit. Because when I removed the red wire and left the white it still came on when either...
  5. C

    2 valves come on at once

    I think I know what might be causing this and will test this weekend. I think I may the red and blue wire may be touching each other somewhere between the controller and valve box causing it to complete the circuit. Because when I removed the red wire and left the white it still came on when...
  6. C

    2 valves come on at once

    Correct. It comes out of the house from the control box then splits only the red, blue and white go to the one valve box and the other colors and white go to the other valve box.
  7. C

    2 valves come on at once

    Would it be the wiring to the solenoid crossed? Because I can trace the blue, red and white all the way back to the control box and it looks good. One thing I did not look at was the white wire in the control box. Could that be messed up some how? I would think that is ok because 2 valves do...
  8. C

    2 valves come on at once

    For some reason I have 2 zones that are coming on at the same time. I have verified at the controller that there is only power to one zone at a time. I then traced the wire to where it comes into the control box and it appears to be wired correctly. Valve 1 has a white and blue wire and valve 2...