  1. A

    Pressure Switch Chatter & Check Valve location

    Epilog: Moving the switch worked. I thought I'd take a brief moment to say thanks to valveman. I moved the pressure switch "down stream" of the check valve and that did the trick. No more chatter. Thanks, Anthony
  2. A

    Pressure Switch Chatter & Check Valve location

    Gary, I have no other check valve between my cistern and the pressure tank. I am not that familiar with jet pumps but I assumed, perhaps incorrectly, without a check valve the pressure tank would just force the water backwards, albeit slowly, through the jet pump once it turned off. Does a jet...
  3. A

    Pressure Switch Chatter & Check Valve location

    OK, I'm a newbie but I promise I did try to answer this question by reading the pevious threads related to chatter first! I just replaced my old pressure pump with a Grundfos 1/2 HP JPS-2A jet pump. This unit comes with SQUARE-D pressure switch attached to the housing, pre-set at 30/50 psi...