  1. R

    Condensate pump output

    Could you please clarify your statement? I'm not sure I understand your comment about what is or is not a code issue. thanks much, rich
  2. R

    Condensate pump output

    Good idea to go with a check valve. But, I have a couple of questions: --Is there such a thing as a check valve for ABS (2" or less)? --With such a small amount of condensate that flows, would a check valve impede water flow into the waste line? I imagine a lot of standing condensate...
  3. R

    Condensate pump output

    Since the furnace is in the basement, and there is neither a sink nor drain below grade, this is not an option (it would be too easy otherwise!). All waste lines are in the open (unfinished) ceiling of the basement. thanks, rich
  4. R

    Condensate pump output

    Thanks for the quick responses. Some clarifications might be in order. Here's the current configuration for my furnace system: furnace ---> 3/4 PVC ---> p-trap ---> 3/4 PVC ---> condensate pump ---> 3/8 flexible copper ---> outside What I'd like to do is re-reroute the condensate out...
  5. R

    Condensate pump output

    Hello all, After spending some time reading about my options, I don't seem to have any definitive solution. So, I'd like to pose this question here: Can I run a 3/8 flexible copper condensate line (from a high-efficiency furnace condensate pump... a Diversitech CP-22) into an ABS waste...
  6. R

    Question about copper/CPVC union

    Ahhh... there be the beast. Ouch, certainly not a cheap hunk of metal. Thanks for the pointer.
  7. R

    Question about copper/CPVC union

    Honestly, I'm just not a fan of compression...anything. Maybe it's just an irrational thing, but I just don't trust 'em. :) That said, given that the 1" trans union that I'm looking at runs @$30 (and I need two of them), it might make sense to give these new-fangled fittings a try. In any...
  8. R

    Question about copper/CPVC union

    I had originally considered going this route, but for 1" copper, it seems I'm very limited in what I've turned up so far (if you can post a link to the 1" trans union that you recommend, I'd be much obliged). To clarify, the filter body is CPVC slip (no thread), and I want to transition to...
  9. R

    Question about copper/CPVC union

    Hello all, I'm installing a spin-down filter off my 1" copper cold-water line. The filter body is 1" CPVC, and I want to use unions so I can disassemble the set-up for maintenance, access to the pressure tank, etc. So, here's my question: Can I take a brass/copper 1" union, toss out...