Does each leg of a 220 line have to have the exact same voltage?

Users who are viewing this thread

LouBrandt

New Member
Messages
4
Reaction score
0
Points
1
Location
Louisiana
Hello,

I have been having some discussions with someone regarding 220 voltage. My question is, do both legs of a 220 circuit have to have the exact same voltage for it to operate? I've always heard that 110 is not always exactly 110, so if that's the case, will a 220 line run ok, if one leg is say 112 and the other 117 or so?

Thanks,
Louis
 

Reach4

Well-Known Member
Messages
38,882
Reaction score
4,433
Points
113
Location
IL
There can be a difference. That would usually be caused by one leg having a lot more load.
 

Reach4

Well-Known Member
Messages
38,882
Reaction score
4,433
Points
113
Location
IL
Yes, but....

I presume these numbers are an example to illustrate the point. In most parts of the US, the nominal voltage is 240/120. That is plus or minus 10%. Being down to 110 would be a bit unusual, but even 108 would still be within spec.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
In a typical US residence, you have 240vac coming in from the transformer. To get 120vac, they put a 'neutral' half-way across the transformer secondary. That's not always placed exactly perfectly, then, the load and wiring can affect the measured voltage you see. Normally, it's close, but rarely exactly the same on both legs to neutral.
 

LBrandt

Member
Messages
48
Reaction score
0
Points
6
Location
Louisiana
In a typical US residence, you have 240vac coming in from the transformer. To get 120vac, they put a 'neutral' half-way across the transformer secondary. That's not always placed exactly perfectly, then, the load and wiring can affect the measured voltage you see. Normally, it's close, but rarely exactly the same on both legs to neutral.

Thanks again.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks