Thanks for getting back to me guys...
Yes, I viewed the spark thru the clear window of the screw-in 20 amp fuse. Don't believe they are delay. They are just regular screw in type fuses...
The ohm reading from the ground to R, Y, and B wires was low. I was expecting an infinite reading but it was about 3 ohms.
I will test the capacitor and see if I can do a diode check...
What type of base does your fuse have, Could you screw a light bulb in it ?
It DOES need to be a time delayed fuse for a motor load. All fuses are not created equal.
Why would you expect a infinite reading, on the motor windings ?
Good Luck