    Question about subpanel

    All advice appreciated Okay...I went with the SP and just finished putting it in place Everything is working perfect. All advice is appreciated Thanks to everyone!!!
  2. W

    Question about subpanel

    Thanks again Okay here is what I am going to do. I have decided to do one or the other of the following depending on cost vs work involved. option one: replace the 30a DP with a 20a SP and move the white wire to the neutral bar in main and thus making my garage on one 20a circuit. option...
  3. W

    Question about subpanel

    Thanks Got it...I'll replace my DP with a SP in the main and do that. Thanks for the good answer....I've asked several people on other sites and I kept on getting vague answers that never helped me. A single circuit is fine I was just trying to make sure I had the circuits there for future use...
  4. W

    Question about subpanel

    I have a 2 wire 240V line running to my garage off a double pole 30 amp breaker from the main panel. This line has no neutral wire. The previous owner had an air compressor dedicated to this line. I have no need for a 240 line running into the garage but I do want 120 for lights and small power...