    Takagi KD-20 Error Code 21

    Make sure the backflow preventer is opening all the way..I have a TKJR and it will work with the backflow preventer in the closed position IE it was stuck shut from small particles that had grown on the vent pipe inside.this was causing a pressure Differential some of the time but it must have...
  2. Tecno

    Takagi Jr Radiant Heat Issue

    Do you have a Backflow preventer installed in the Exhaust pipe?? if so make sure that it can move freely.I have one on my unit and i found that it had stuck shut my bad should have done the yearly check on the unit I cleaned out the pipe and made sure that it moved freely and it fixed the problem.