    Do I need a primary loop? (Lochinvar Knight)

    Thank you for having the time to answer. In terms of calculations and math, the data is quite simple in our case: -33 kBTU max heat load -only one heating circuit (no need for DHW) -system design temp of 20F, this making it 3.0 GPM needed flow rate -the max flow rate for Lochinvar Knight...
  2. smihaila

    Do I need a primary loop? (Lochinvar Knight)

    Hi BadgerBoilerMN, I am planning to have the same Lochinvar model WHN055 installed at my house. The Manual J calculation shows a heat loss of 34 kBTU, so a boiler with max 55 kBTU and featuring a 5:1 downturn conversion factor (i.e able to fire for heat demands of at least 11 kBTU - which...