Recent content by Scott McNab

  1. Scott McNab

    Boiler Temperature

    Right now it's $1.05 per liter for oil and I pay $.63 per liter for propane. I have last winters oil numbers so I'll have to compare with this winters propane. Of course a different boiler too. I guess if it's more expensive I'll have to find an experienced hydronic installer to help find a...
  2. Scott McNab

    Boiler Temperature

    It maintains 18 degrees. House isn't insulated great so any warmer would likely get quite expensive. I'm just used to oil so it seems like I'm burning a lot of propane. Seems I'm worse off. Temperature swing doesn't really bother me. It does drop 1 degree as the boiler is burning until the...
  3. Scott McNab

    Boiler Temperature

    What can I do short of replacing the boiler if I don't have enough emitters?
  4. Scott McNab

    Boiler Temperature

    So 20 minute burn, off for 20-30 minutes and repeat cycle is ok? That's with a -20 degree celcius day. Warmer days the idle times are longer. No matter the outdoor temperature, the burn time is always 20 minutes to satisfy thermostat.
  5. Scott McNab

    Boiler Temperature

    As it's a low mass boiler, once the burner is off and circulator running, the water in the system gets cool quite quickly. I actually liked my high mass oil boiler better. Water stayed hot for a long time even when circulating. So far this boiler has been a disappointment.
  6. Scott McNab

    Boiler Temperature

    That's how it works. Only other control is a high limit set at 200 to kill the burner if it gets that hot. The burner heats the 4.5 gallons quickly but once the circulator starts it slows down considerably. High limit would kick the burner off but it has its own differential. Thermostat...
  7. Scott McNab

    Boiler Temperature

    The burns are 20 minutes average. Once the thermostat is satisfied then it doesn't fire for roughly another 20-30 minutes when really cold and the cycle repeats. Yes the L6006C is only controlling the circulator. The home thermostat controls the burner. At first it was set up where the aquastat...
  8. Scott McNab

    Boiler Temperature

    Boiler is Biasi B10 series Model B-4. Gross Input M.B.H 126, Gross Output M.B.H 110. Circulator is Bell and Gossett K20. Aquastat is Honeywell Type L6006C. Burner is LP gas Riello 40 N12OS. 85' feet of Slant Fin 30 baseboard rad.
  9. Scott McNab

    Boiler Temperature

    One thermostat, so single zone.
  10. Scott McNab

    Boiler Temperature

    Yes I'll get you that information tonight. It branches off into different zones but comes back as one. I believe it's considered one zone. What would make it a single zone or multiple zones?
  11. Scott McNab

    Boiler Temperature

    Hopefully it will help with efficiency changing to 145 and 15 differential as opposed to 30 differential. Any bit helps.
  12. Scott McNab

    Boiler Temperature

    Sounds good. Thanks for your help. I'll change the settings when I'm home and we'll see what happens. I may be asking more questions. Thanks again
  13. Scott McNab

    Boiler Temperature

    The masonry chimney has a new aluminum liner. So you think I should start with the circulator to come on at 145 and set the differential to 15? Or would say 160 and differential of 30 be any better? Or wasteful?
  14. Scott McNab

    Boiler Temperature

    Would just be a lot of starting and stopping for the circulator as the cool water in the rads will rush back when the circulator pump turns on and the aquastat would shut it off at 130 until the boiler reaches 145 again. Continuous cycle until the water stays above 130 and the aquastat leaves...
  15. Scott McNab

    Boiler Temperature

    It doesn't cycle the burner during a call for heat. Just gets up to temperature where the thermostat is satisfied and shuts off which must mean the rads are getting rid of the heat quick enough. Water temperatures range from I'd say 140 to 180 when the boiler shuts off, depending on the outside...
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks