Recent content by Rrm8711

  1. R

    Tankless Challenges

    Thx for the reply Turned control panel off Turned off power supply Unplugged unit Removed screen Reset dip-switches to LPG Plugged unit back in Turned on power supply to unit Turned on unit at control panel Turned on hot water at bath & let it cycle (4 x’s) No fire up.
  2. R

    Tankless Challenges

    Thx for the reply. Old 2nd stage regulator is Rego LV4403B66R. Replaced with same. In reading Rego website info, they set their regulators at the factory to 11”. I took 2 readings today at the regulator - average was 11.11”, so I’m content with that. Pressure reading at the inlet port at the...
  3. R

    Tankless Challenges

    Thx for the reply. Dip-switch settings: 1on/2off for LPG 3-4-5 on for elevation range 7,501-10,100 ( my area is 8,700) 6 on, 7-8 off for single exhaust vent & room-air intake. I don’t think there’s any blockage on the exhaust vent, for when I’m troubleshooting with the front water heater cover...
  4. R

    Tankless Challenges

    Thx for the reply. -Picture’s of what specifically? I have tried uploading some pictures previously, but are denied because the file is too big. -I’m not familiar with what a gas takeoff is; unless my propane supplier tech’s did one when they were out on 4/12?…IDK -I installed the new Takagi...
  5. R

    Tankless Challenges

    Update: I was hoping I would be texting about my tankless water heater problems solved; not the case. Just a rehash- since 3/26, the newly installed Takagi 310U won’t work consistently. My propane supplier sent a couple of techs out (4/12) to look at the second stage regulator and water...
  6. R

    Tankless Challenges

    Update: I bought both a digital & water manometer. Hooked the water type up to the inlet port of the water heater for a static reading & it responded like a geyser when I turned the gas supply valve on. Then hooked up the digital and it was over 20” WC , so there is definitely something going...
  7. R

    Tankless Challenges

    Yes, the regulator is rated for LP. The house is 24 years old (I’ve been in it 4 years) and It’s been on propane since being built. I’m hoping it’s the second stage regulator- there’s nothing else between it & the water heater.
  8. R

    Tankless Challenges

    Thank you for your reply. If you are referring to the/these manifold pressure numbers, then yes 310U Indoor: Max: 2.42 to 3.00/ Min: 0.41 to 0.52. When my propane supplier tech comes out to install the new 2nd stage regulator, I’ll have him verify the 1st stage. Then will have him check and...
  9. R

    Tankless Challenges

    Whoops. Says file is too big to upload
  10. R

    Tankless Challenges

    Combustion area of the old unit.
  11. R

    Tankless Challenges

    LP tank is 1k gal @ 85% capacity. Just some footnotes: -The previous tankless water heater that I replaced was 199K BTU unit and was 21 years old. -The previous owners had the dip switches set to 140° (Default on this older model is 122° ,according to the manual). So the unit ran fine at 140°...