Recent content by Igor

  1. Igor

    Self-Contained Switches/Receptacles in Mobile Home

    You can find the instructions for one commonly-used brand of self-contained devices here: Wirecon Installation Guide. Note that the end of the document mentions some ways to install the device without using the expensive installation tool. I believe Pass & Seymour manufactures a similar line...
  2. Igor

    Emergency Generator Test with questionable results

    My guess is that the neutral and one of the hots were swapped somewhere, so those 120V transformers were getting 240V.
  3. Igor

    33 amp, 3-phase Clothes Dryer

    No. Three-phase power is usually available only in commercial and industrial buildings. It would be quite unusual for a home to have three-phase power. It is possible to install a phase converter to convert single-phase to three-phase, but I doubt that it would be economically practical.
  4. Igor

    low voltage wiring?

    It depends on where you are. Many states do require licensing for low-voltage work; some don't.
  5. Igor

    Christmas light question

    My guess is that there's some kind of shunt device built into the socket that's not working. The shunt is supposed to bypass a burned-out filament and allow the rest of the string of lights to keep working when one bulb burns out. Shunts are not very reliable. You can buy a "zapper" that will...
  6. Igor

    Help with electric heater connection!!

    Quite correct, and fixed electric heaters are considered to be a continuous load. The NEC is available online for free (although you have to register) viewing at the NFPA.org website. Article 424 covers Fixed Electric Space-Heating Equipment. 220.19(A)(1) & 220.20(A) deal with continuous...
  7. Igor

    Oven Blew Up at Connector with Element

    It's possible that the failure is right at the end of the wire where it connects to the element. If you're lucky, there may be enough slack in the wire to cut off the damaged end of the wire and crimp on a new connector. The usual Faston-type connector that you can buy at a hardware store won't...
  8. Igor

    Working length of wire

    The NEC (300.14) requires at least 6" of free conductor, measured from the point where the conductor emerges from the cable sheath or raceway, and also the conductors must extend at least 3" from the opening in the box, if any dimension of the opening is less than 8". Note that the 6" is not...
  9. Igor

    Ground wire

    You can run Romex in EMT if you meet the fill requirements, although usually you wouldn't except for short lengths for protection from damage. I haven't done the math, but I suspect you need something bigger than 1/2" EMT (see Chapter 9, Table 1, Note 9 for the fill calculations.) You should be...
  10. Igor

    Ground wire

    Was your existing wiring armored cable or in metallic conduit? If so, the conduit or armor serves as the grounding conductor.
  11. Igor

    Phantom voltage

    Some of the newer Fluke Digital meters have a low-impedance mode to avoid this problem. I'm not sure if other manufacturers have come out with similar products yet.
  12. Igor

    Box make up

    The NEC requires not less than 1/4" of sheathing inside the box (314.17 (C), 2005 edition.) There is no maximum length of sheathing stated, however if you leave too much sheathing you may not have the 6" minimum length of free conductor required by 300.14, which is measured from the end of the...
  13. Igor

    What is the name of the tool??

    That "Nut Twister" looks like it's meant to twist the wire nut, not twist the wires before installing the nut. There are other tools out there that will do the same thing; some Ideal screwdrivers have a wire nut wrench in the handle, and you can get wire nut bits for a cordless drill.
  14. Igor

    What is the name of the tool??

    No, those are for stainless steel safety wire. The safety wire is run through holes drilled in nuts and bolts to keep them from vibrating loose. I don't know of anything like the OP describes that is currently on the market, but there is a patent for a wire-twisting device.
  15. Igor

    Replace weatherhead without turning off service?

    The risk is more than just being "zapped." The POCO transformer can supply a very large amount of current, perhaps 10,000 amps, in the event of a fault. If you've ever seen an arc welder at work, that arc is only about 100A. If your service wires short while you're working near them, you may be...