Recent content by gennady

  1. gennady

    Old house with oil/steam heat - help

    Sure VFD or at least bypass pressure differential. VFD will decrease flow trough system and boiler without separation when load will drop. Differential pressure by pass will keep same max flow trough the boiler even system flow might be very low, if there is no separation when load will drop...
  2. gennady

    Old house with oil/steam heat - help

    Are you even reading my posts?
  3. gennady

    Old house with oil/steam heat - help

    Maybe now is the time to read this book?
  4. gennady

    Old house with oil/steam heat - help

    So, if you using TRVs, do you use p/s or you still using direct pumping ? Also buderus , Weil McLain and slant fin are great brand names and I feel good you some how place me in that group in regards of single minded average plumber I am. So still do you use TRVs with direct pumped boiler ?
  5. gennady

    boiler 200000 btu

    Find qualified installer with good track record and references, and he will guide you trough whole process. Just place price issue at #5 in your priorities list in this project.
  6. gennady

    Old house with oil/steam heat - help

    Quote Originally Posted by BadgerBoilerMN QUOTE: Viessmann does not mandate P/S and one of the reasons they are one of our favorites on steam and gravity conversions. They do like to sell hydrolic separators, something trade magazines and those who write for them are sensitive to. There...
  7. gennady

    Old house with oil/steam heat - help

    Usually $20k+ only boiler with indirect. Steam to hot water with mod con boiler and indirect for 20K is below the cost in my opinion.
  8. gennady

    Old house with oil/steam heat - help

    where in my post "these are clear guidelines for LLH also make a note that in viessmann opinion primary secondary arrangement does promote condensing in condensing boilers, quite different from your statement." you see words viessmann mandates? Also see all benefits listed. Why not do it...
  9. gennady

    Old house with oil/steam heat - help

    It costs much more than $20.000 to do steam to hot water conversion properly
  10. gennady

    Old house with oil/steam heat - help

    This is not true. load is determined by space heat loss, not temperature of radiator. Also, delivering higher temperature water to radiator or manifold, allows to cut on flow, because heat load is dictated by heat loss, and using universal formula Q=dTxFlow(GPM) x500, where Q is amount of heat...
  11. gennady

    Old house with oil/steam heat - help

    these are clear guidelines for LLH also make a note that in viessmann opinion primary secondary arrangement does promote condensing in condensing boilers, quite different from your statement.
  12. gennady

    Old house with oil/steam heat - help

    Well insulated steam pipes losing as little heat as well insulated hot water piping. It does not matter what diameter piping there, it matters how well piping insulation done in unconditioned spaces. And we do it well. Heat losses of uninsulated brownstones are high, but does heat loss depends...
  13. gennady

    Old house with oil/steam heat - help

    Maybe you need this book signed by Dan Hologan I attached photo of afterword page. Interesting reading, isn't it? BTW, last time I saw Dan, he thanked me for contribution to his site. And this page is from viessman vitodens boiler installation manual. This boiler is so new, it will...
  14. gennady

    Old house with oil/steam heat - help

    Why you discriminating against elderly people and cats? They can be burnt by hot radiator too. And what about a cup of tea? What if children are around cup of tea of 200F. They can get burnt too. Steam is around for a quite a few years and i still have to hear about children burnt by hot...
  15. gennady

    Old house with oil/steam heat - help

    Btu is btu. What gets lost trough envelope of building gets replenished by radiator output. When balance loss/gain is reached temperature in the room gets stable. Your reference to lower radiator temperature on forced hot water system probably is outdoor reset, on steam I use indoor reset. High...