Hi i have been reading about prolonged wait time for hot water.
this is the same experience i’m having with the Navien240A,
All new copper system, I am using
cold line with Grundfos value in furthest vanity for recirculating.
The valve is set to recirculate, DIP 2 on peramitor 17 on. Photo shows plumbing with check valve. Tenant still says wait time is over 2min. and water to shower not full hot. about 64 lf of copper. am i missing something?
upload_2020-11-16_10-41-23.jpeg
 

Bannerman

Well-Known Member
Messages
4,874
Reaction score
804
Points
113
Location
Ontario, Canada
Last edited:

Breplum

Licensed plumbing contractor
Messages
2,010
Reaction score
832
Points
113
Location
San Francisco Bay Area
Have you enabled thermal bypass valve parameters (P17)?
Set the 2-way valve to External.
Adjust pump cycle interval time maybe (P12)?
I see you did not install either of the recommended shut off valves on the return line. Not recommended. You want to be able to both service that flex line if needed. The NavCirc is designed for Navien's function better than Grundfos'.
 

bigdevil

New Member
Messages
8
Reaction score
0
Points
1
Location
California

bigdevil

New Member
Messages
8
Reaction score
0
Points
1
Location
California
Have you enabled thermal bypass valve parameters (P17)?
Set the 2-way valve to External.
Adjust pump cycle interval time maybe (P12)?
I see you did not install either of the recommended shut off valves on the return line. Not recommended. You want to be able to both service that flex line if needed. The NavCirc is designed for Navien's function better than Grundfos'.
Thanks i didn’t change P 12 it is default now should i change value?
 

Bannerman

Well-Known Member
Messages
4,874
Reaction score
804
Points
113
Location
Ontario, Canada
Although your return valve is not Navien's, the settings appropriate for a cold water return loop are specified in the NaviCirc manual at the link provided.
 

bigdevil

New Member
Messages
8
Reaction score
0
Points
1
Location
California
Although your return valve is not Navien's, the settings appropriate for a cold water return loop are specified in the NaviCirc manual at the link provided.
What do you think about P 12 it is at default 20 minutes should i reduce time? would that increase hot water duration? Thanks
 

Bannerman

Well-Known Member
Messages
4,874
Reaction score
804
Points
113
Location
Ontario, Canada
The setting used when utilizing a Hot Button to activate the pump is 5 minutes. I haven't searched to compare the flow rate for the Grundfos valve vs the NaviCirc but you might attempt a 5-minute setting to determine if sufficient for hot water to arrive at the Grundfos location. Every home's piping configuration is unique so if 5 minutes is longer than needed or insufficient, then the setting could be altered by 1-minute at a time to reevaluate the following day.

As these valves utilize the home's cold water plumbing lines for the return loop back to the water heater, the valve is designed to shut off return flow once sensing only 95-100℉ otherwise the cold water lines will become too warm. Because the return valve will be stopping flow at that temperature, do not expect the hot water from the faucet will be initially very hot even with a substantially higher WH temperature setting or longer run time for the pump.
 
Last edited:

bigdevil

New Member
Messages
8
Reaction score
0
Points
1
Location
California
The setting used when utilizing a Hot Button to activate the pump is 5 minutes. I haven't searched to compare the flow rate for the Grundfos valve vs the NaviCirc but you might attempt a 5-minute setting to determine if sufficient for hot water to arrive at the Grundfos location. Every home's piping configuration is unique so if 5 minutes is longer than needed or insufficient, then the setting could be altered by 1-minute at a time to reevaluate the following day.

As these valves utilize the home's cold water plumbing lines for the return loop back to the water heater, the valve is designed to shut off return flow once sensing only 95-100℉ otherwise the cold water lines will become too warm. Because the return valve will be stopping flow at that temperature, do not expect the hot water from the faucet will be initially very hot even with a substantially higher WH temperature setting or longer run time for the pump.
thanks
 

bigdevil

New Member
Messages
8
Reaction score
0
Points
1
Location
California
Thank you that was helpful.
I have a new related question.
The tenant is saying she hears a
“ wirring” sounds at the bathroom at night. Does anyone know is the Grundfos valve could make a sound like that? I inspected installation and valve was secure and only heard faint water running sounds during pump cycles.