water heater over temp (T & P ) valve piping question

Users who are viewing this thread

Npreiser

New Member
Messages
2
Reaction score
0
Points
1
Location
Oregon
During home inspection, I found that the hot water heater T&P valve piping used cpvc(not copper) , which
is supposedly OK. The piping from the T&P value turns in the upward direction, for over 4+ feet, going 2+ feet above the top of the hot water heater,
then goes horizontal...and then down, to a drain, with a total run well over 25ft

Reading online and the manual for the heater says that the piping should allow gravity feed, which
implies it should never go upward.

Any suggestions/opinions would be greatly appreciated..
Is this acceptable?

This is a replacement heater in a 1950s home ,in a location that did not include a drain(hence the nonstandard install).



Nick .
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
"Is this acceptable? "

Not in my city. It should be all 3/4" copper, drain to the outside, no more than 6" above grade.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
I see plenty of CPVC relief lines run in Seattle and approved by the inspectors.
However, they all run downhill.

If we have a situation where we can't drain them downhill, we still run the relief down from the water heater.
As high as we need to be, we place a 125 PSI relief in a location where we can drain it.
This may be on the cold line. The idea being that this opens before the T&P on the water heater. The water heater T&P may never, ever need to open up if you have a 125 PSI relief on the incoming cold.
 
Last edited:

Reach4

Well-Known Member
Messages
38,749
Reaction score
4,400
Points
113
Location
IL
I have a hard time seeing how going a few feet uphill rather than relying on gravity is going to conceivably cause a problem. I guess it would be some condition where you had over-temp but not pressurized?

On a different note npreiser, what software is it that changes "valve" into "value"? I have seen that substitution made several times before.

dj2, maybe this would be a good application for galvanized in your city, but you probably don't carry that. :)
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
I have a hard time seeing how going a few feet uphill rather than relying on gravity is going to conceivably cause a problem.

If you have leakage from the T&P and it can't drain out, it can become blocked over time and useless.
First rule of plumbing, it all has to go downhill.

A water heater with a blocked or plugged T&P has been known to explode through the roof and land blocks away. It's rather serious.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
I have a hard time seeing how going a few feet uphill rather than relying on gravity is going to conceivably cause a problem. I guess it would be some condition where you had over-temp but not pressurized?

On a different note npreiser, what software is it that changes "valve" into "value"? I have seen that substitution made several times before.

dj2, maybe this would be a good application for galvanized in your city, but you probably don't carry that. :)


On another site I am catching all sorts of hell for useing cpvc
on my t+p drain line... even though it is ok in Seattle and most parts of the country everyone over there thinks their code is the best......

mark_tp_lime.jpg


The real problem with running the t+p uphill from the heater is over time the line could fill up with water.... once it begins to fill up with water , the water becomes soiled with bacteria and other nasties.... stagnant water....

If the t+p is leaking and the water is ever turned off in the system
there can be a back pressure or siphonage through that t+p and all the nasty water that has been laying in that line will suck back into the water heater.........

Correct me if I am wrong but I think that is called a potential
cross connection ....and if it makes anyone sick or not depends on the situation... I dont know how much botulism or bacteria it would take to make someone sick if they were to brush their teeth with hot water or whatever....
 
Last edited by a moderator:

Reach4

Well-Known Member
Messages
38,749
Reaction score
4,400
Points
113
Location
IL
You and Terry have stated good and logical reasons. My thought that there was going to be plenty of pressure to drive the water uphill had flaws.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; I have a hard time seeing how going a few feet uphill rather than relying on gravity is going to conceivably cause a problem. I guess it would be some condition where you had over-temp but not pressurized?

The real problem is that the T&P valve has a metal spring. If the discharge goes "uphill" the spring is ALWAYS in the water and WILL corrode to the point where it either cannot open or cannot withstand the system's pressure. A secondary consideration is that in certain conditions the trapped water could freeze making the valve inoperative.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
As far as the CPVC goes, here, they take the requirement that the discharge be "full size" literally which means that 3/4" CPVC is NOT 'full size'. We cannot even use a water heater flex line because the corrugations reduce it to less than "full size".
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
As far as the CPVC goes, here, they take the requirement that the discharge be "full size" literally which means that 3/4" CPVC is NOT 'full size'. We cannot even use a water heater flex line because the corrugations reduce it to less than "full size".





that is a bummer..... We use the cpvc all the time and it appears to
be full size to me,, unless they are quibbling over 2/62nd of an inch
I always heard they did not care for cpvc because of the scalding water issues through the t+p valve.......

I use the flex lines all the time on the heaters in our town with no issues
what so ever.... I dont understand what the difference is considering
if it goes through a water softener it usually gets reduced down under a
half an inch ... And of course it gets reduced down to 3/8 at most faucets..

 

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
Some places want the T&P to go outside. Places that require this may have provisions for when this isn't practical. I've seen documentation for cities in Calif. to run the T&P uphill, for instance. Here is an example:

http://www.cityofpaloalto.org/civicax/filebank/documents/17800

In this case, they use a small drip line off of the T&P discharge to detect small leaks.

In terms of CPVC, the OD is the same as copper, but the ID is smaller. So, if the WH is fed with 3/4" copper, then an inspector may say the CPVC on the T&P is not "full size". If the whole house is CPVC, I don't see how they could make the same argument..but they may try anyway. :)
 