What is the current code regarding the following related to requiring GFCI Protection.


50 gal Water heater, hard wired to 30a 220v
1 1/2 HP Pool pump, hard wired to 20a 220v (in ground pool)
5 ton, Pool heat pump, hard wired to 50a 220v (in ground pool)
 
Last edited:

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
Looks like No, Yes, No.

Florida is on 2008 NEC unless you have additional local requirements.

680.22
(B) GFCI Protection. Outlets supplying pool pump motors
from branch circuits with short-circuit and ground-fault
protection rated 15 or 20 amperes, 125 volt or 240 volt,
single phase, whether by receptacle or direct connection,
shall be provided with ground-fault circuit-interrupter protection
for personnel.
 
Last edited:

JerryR

Active Member
Messages
584
Reaction score
41
Points
28
Location
Florida
Follow up question.

In ground a Gunite Concrete Pool was constructed in 1997 when code did not require a GFCI for the pump motor.

Is it worthwhile and cost effective to replace the pump breaker with a $110 GFCI breaker? (20 amp dual pole, Square D QO)

Actually I just realized I would need to replace 2 breakers as the Jet Pump for the spa is also on a standard 20a breaker.

What is the consensus of members?
Is a GFCI overkill?
What risk is there of nuisance tripping? This I a concern because we are gone for 7-10 days sometimes.

I think know what I probably will do.

The pool and pool equipment are all properly bonded.
 
Last edited:

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
Wasn't required in 1997. Code started in 2008 for hard-wired pumps.

Yes, there is increased risk of nuisance tripping if bad motor. Otherwise one less chance of electrocution.

Proper bonding gives a better route for current to flow/easier for a breaker to trip.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
No
Yes
YES. A pool heater heat pump is still a motor associated with the pool. GFI protection required.
 

JerryR

Active Member
Messages
584
Reaction score
41
Points
28
Location
Florida
No
Yes
YES. A pool heater heat pump is still a motor associated with the pool. GFI protection required.

This is confusing. That's why I posted my question. I don't know how pros keep up with this stuff.

Florida is on 2008 NEC code. Look at this link from NEMA.org.
http://www.nema.org/Technical/Code-Alerts/Pages/Code-Alert-Florida-28-September-2009.aspx

From what read 680.22(B) states GFCI required for 120 240v 15-20 amp pump motors. Heater is on a 50 amp breaker. Wouldn't that exclude this heat pump from requiring a GFCI breaker?

Even so, according to the NEMA link, Florida adopted 2008 code but excluded 680.22(B) requirement for GFCI for single and double family residences even with 15a and 20a pumps.
 
Last edited:

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
YOu can do what you want to, but I personally would NEVER connect a "necessary" motor such as a refrigerator/freezer, pool pump, etc., to a GFCI, which could "nuisance" trip and cause possible irreparable damages.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
YOu can do what you want to, but I personally would NEVER connect a "necessary" motor such as a refrigerator/freezer, pool pump, etc., to a GFCI, which could "nuisance" trip and cause possible irreparable damages.

Loss of life is not irreparable damages? Much safer to lose some food than your life...
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
YOu can do what you want to, but I personally would NEVER connect a "necessary" motor such as a refrigerator/freezer, pool pump, etc., to a GFCI, which could "nuisance" trip and cause possible irreparable damages.

You CANNOT be serious!
With as much good as I have seen posted from you over the years I cannot believe you posted this.
 

JerryR

Active Member
Messages
584
Reaction score
41
Points
28
Location
Florida
You CANNOT be serious!

It seems that Florida Building Commission agrees with HJ. They adopted the 2008 NEC code but exempt GFCI on residential pools. (one and two family dwellings)
http://www.floridapoolpro.com/indus...es/FL Building Commission adopts 2008 NEC.pdf

They felt that GFCI "would not have provided any additional benefit. Rather requiring GFCI would have caused nuisance trips on the pool pump, increasing safety and health issues as pools would not be circulating"

And then there is this from NEMA
http://www.nema.org/Technical/Code-Alerts/Pages/Code-Alert-Florida-28-September-2009.aspx
 
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
do research to find out that Florida has more pool shocks than all the other states added together.



In my opinion everything should be GFCI protected, come to my house and you will see
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
The LAST thing I would do is use the state of Florida as an example of quality electrical work.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
FL seems to allow you to build a shower without a liner...just weeps into the sand beneath the foundation and provides moisture for the termites and invites tree roots into your home! The rest of the country requires a sloped liner to the drain. If you search around, you'll find lots of pictures of torn out showers with rotten wood, encased in roots, and other issues...I agree, FL is not a good example for the building trades and practices.
 