120 PSI fresh water from town - Going to install a PRV

Users who are viewing this thread

Philtrap

Member
Messages
90
Reaction score
0
Points
6
Location
Long Island, NY
Folks,

I have a 50 year old home with no fresh water pressure reducing valves (PRV) installed. I found this out after my garden hoses kept blowing and I checked the pressure which is at 120 psi at all the outside spigots and the sinks inside where I could thread on the pressure tester. I've tested the pressure at all times and it's always 120 psi or close to it. There is no PRV after the meter and I'm not sure if there is a faulty one the town installed underground somewhere before the meter (which is in my basement), but I doubt there is one. Anyway, a quick question...

I have a lawn sprinkler system that works great. If I reduce the incoming pressure from 120 psi to 50 PSI (the factor set for the PRV) right after the meter, do you think the sprinklers will work the same or will I have to make adjustments to them? The PRV I'm planing on installing would be before the sprinkler system just after the meter... I could install the PRV after the sprinkler system since it's teed off after the meter on it's own line, but there is one spigot on that line too and the hoses on that would keep blistering and blowing if it wasn't regulated.


Thanks in advance
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
If you have any valves on the irrigation, the 120 psi will be too much for them too.
It may not be a bad idea to have a PRV for the home and one for the irrigation.
Code requires pressure reduction for anything over 80 PSI
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
While the PRVs do come preset from the factory, that doesn't mean that they are not adjustable. Residential plumbing fixtures are designed with the 80psi in mind, and have a decent margin of protection when it gets higher, but it's best not to test them on a regular basis!

Keep in mind that adding a PRV requires adding an expansion tank to account for the fact that makes the system 'closed', and when you heat water, when it expands, it needs a place to go.
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
Install a separate PRV for the sprinkler system, and set it at 75.
We do it all the time.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Install a separate PRV for the sprinkler system, and set it at 75.
We do it all the time.



That would work better, especially if you want to use both at the same time.
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
Even a lower pressure would not be a bad idea for the house supply. Mine is set a 50 psi and that seems to be quiet enough for me. Expansion tank is a must.
 

Philtrap

Member
Messages
90
Reaction score
0
Points
6
Location
Long Island, NY
I have an expansion tank right before the hot water heater on the cold water side. Is this the one you guys say is a must???
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
The lawn sprinkler system complicates matters, if the installer designed the system to depend on the high flow the 120 psi supply would provide. There are sprinkler systems that end up requiring extensive reworking, if something is installed in the supply line that significantly cuts pressure and flow.

A standard PRV comes with a high insertion loss. Charts that display friction loss through a PRV almost always base the performance curve on their being a minimum of 50 psi pressure reduction through the PRV. Any standard PRV that is only partially opened (when you don't have the full 50 psi loss set up) will have much more pressure loss than the charts would suggest.

What can work best for regulating lawn sprinkler system pressure is pressure-regulating master valve, which doesn't kill the pressure (beyond your adjustment of the output setting) and flow in a sprinkler system. Most every major sprinkler manufacturer has one or more of these in their product offerings, and they often cost less than a standard brass PRV.
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
Wet_Boots,

I live in an area where the street water pressure is 150 in the flat areas and more than that in the rolling hills.

Folks who don't have a PRV in their sprinkler system, experience leaks.

I own a rental on a hill, where I have to replace the PRVs every 5-6 years. Last week I replaced 2 of them for customers. I install Wilkins regulators only, not plastic crap.

BTW, since January 1, 2013, all PRVs sold in CA must be "lead free". But that's another issue.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
BTW, since January 1, 2013, all PRVs sold in CA must be "lead free". But that's another issue.


They did the same BS for Foot Valves.


Time will tell... The way people on Earth are acting, there may not be much time left.
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
I don't mind making my home "lead free" or "99% lead free". But when I get my water from 80 year old galvanized city pipes...where's the logic?
 

Philtrap

Member
Messages
90
Reaction score
0
Points
6
Location
Long Island, NY
Wet_boots, A question for ya...

... if the installer designed the system to depend on the high flow the 120 psi supply would provide...


Would a sprinkler installer design it at 120psi? Isn't that too high for the heads and the zone valves? I'm just asking and I'm not sure much design went into the irrigation system other than the guy saying I have enough pressure and he'll put the heads in "these" spots to make full coverage. BTY, I tested the biggest zone today after installing the PRV which I adjusted to 60psi and it seemed to work fine. They didn't spray as far, but they still hit all the grass. Most of them overlap some so I think it should be fine running at 60psi.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I don't mind making my home "lead free" or "99% lead free". But when I get my water from 80 year old galvanized city pipes...where's the logic?


lol


Them old pipes must be why everyone is going Nuts.

Kind of late to fix them now.
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
Wet_boots, A question for ya...




Would a sprinkler installer design it at 120psi? Isn't that too high for the heads and the zone valves? I'm just asking and I'm not sure much design went into the irrigation system other than the guy saying I have enough pressure and he'll put the heads in "these" spots to make full coverage. BTY, I tested the biggest zone today after installing the PRV which I adjusted to 60psi and it seemed to work fine. They didn't spray as far, but they still hit all the grass. Most of them overlap some so I think it should be fine running at 60psi.
Sight unseen, there isn't any way to know for sure. To be able to cut in a PRV into an existing sprinkler system and not have it suffer catastrophic loss of performance requires that the existing sprinkler system have pressures in the zones that are 20 psi more than required. Basically, every head would be over-pressured to the point of generating visible misting.

Installers typically aren't leaving any available flow under-utilized. There is real value in getting the watering done in a minimum of time. I would never, ever, assume the ability exists to cut in a standard PRV on any existing sprinkler system.

Understand that the supply pressure is never getting to the sprinkler heads. By the time water flows through the meter and supply line, into the sprinkler system and through a backflow preventer, the 120 psi you measured with the system not running drops below 100 psi. In the homes I deal with, having water meters in the basement, the pressure loss in the supply line to the house is a big factor.

When I do see a genuine need to reduce sprinkler zone pressure beyond what a flow control on each zone valve can provide, then it is the regulating master valve I employ, because it alone is capable of sustaining full flows in the sprinkler system.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Wet_boots, A question for ya...




Would a sprinkler installer design it at 120psi? Isn't that too high for the heads and the zone valves? I'm just asking and I'm not sure much design went into the irrigation system other than the guy saying I have enough pressure and he'll put the heads in "these" spots to make full coverage. BTY, I tested the biggest zone today after installing the PRV which I adjusted to 60psi and it seemed to work fine. They didn't spray as far, but they still hit all the grass. Most of them overlap some so I think it should be fine running at 60psi.


For a House that old I would bet it was not designed for 120psi.

Flow and volume is more important than pressure, Because as soon as the heads start spraying the pressure drops, then you want volume and a pressure of 60 psi is fine.


Have Fun.
 

Wet_Boots

Sprinkler Guy
Messages
799
Reaction score
2
Points
16
Location
Metro NYC
The age of the sprinkler system figures into things as well. Since modern design practices call for more sprinkler heads placed closer together, with each head spraying onto the next head down the line, such systems are much more tolerant of a pressure loss than are older systems, that counted on a head spraying the 40 feet it was intended to, and not a few feet less.

120 psi is not higher in pressure than any sprinkler zone valve's pressure rating. Most of them are rated 150 psi, and top models can have 200 psi ratings. In practical terms, 120 psi is around the point where you would have a PRV in the system supply (like a Wilkins BR-4 set at 80 psi)

What a PRV does more than anything, for a sprinkler system, is to cut down on water hammer when zone valves close. Quieter plumbing makes for happier customers.
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
No where in this discussion do I see any mention of back flow prevention. It seems everything just tees off the line from the meter. I realize the problem in point is the excess pressure, but unless you have a back flow prevention device for the irrigation line, you should look into this.
 

Philtrap

Member
Messages
90
Reaction score
0
Points
6
Location
Long Island, NY
No where in this discussion do I see any mention of back flow prevention. It seems everything just tees off the line from the meter. I realize the problem in point is the excess pressure, but unless you have a back flow prevention device for the irrigation line, you should look into this.

Gary - Thanks... The irrigation system does have a Watts back flow preventer valve.
 