I am adding a half bath on the first floor and a 3/4 bath on the second. They are stacked above and below each other. It will be all new plumbing on the left side branch of my drawing. Do you see any problems with my venting of the two baths together using a 3" stack? What fittings are necessary for the connections on each floor?

Horizontal distance from new stack (on the left) to main(original) CI stack where I will tie in is about 7feet. The new WC on the second floor will be about 3feet from the new stack so horizontal distance will be right around 10 feet total after all the drop.

Long sweep at bottom of new stack with cleanout wye above?

Sinks=1 1/2", shower 2" and "3 inch for stack and WC to the basement.


two new bathrooms plumbing.jpg
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
Any wet venting has to be on the same floor, a bathroom group in a residence.

The toilet vent, or wet vent needs to happen before the waste from upstairs enters the line.
So the downstairs lav would need to wye in closer to the downstairs toilet, "before" the wye for the upstairs bath.

Also, the upstairs shower needs a vent between the it's trap arm and the stack below the toilet.
The vent needs to come off the top of the trap arm, you can't go up after a vent, except for the normal 1/4" per foot grade, within five feet.

Longer then that, not allowed
More grade then that, not allowed.
 
Last edited:

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
First floor wet venting

First floor wet venting of WC using sink (2") so that the venting is before the y. Vent connects above flood level on second floor. Correct?

Does it need a vent where it finally turns vertical to tie in at the main stack in the basement? (Red hand pointing to the 90 elbow at the bottom of the drawing.)

both levels.jpg
 
Last edited:

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
Venting the shower upstairs

See my options for venting the shower a couple posts below.
 
Last edited:

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
Wondering if adding a vent for the WC before the wye that connects the lav is a good option?
 
Last edited:

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
New questions and new drawing

Going back to the original drawing to work things out. Thank you hj for steering me away from the albatross.
 

Attachments

  • both levels.jpg
    both levels.jpg
    36 KB · Views: 9,643
Last edited:

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
You started with a "simple" design which needed a few revisions and have created a "monster". The "second" drawing is completely wrong because you cannot connect the vent back below the upstairs bath. From you drawing it appears you are putting the pipes below the joists so you can use a side inlet "T" for the lav and shower inlet. This is NOT the place to give you a tutorial on installing drains and vents, but if it were I, I might throw your entire drawings away and start over with a much simpler design than any of them.
 

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
I understand this is not a tutorial site. Too much time last night I guess. I was searching the forum for examples and found someone else's example that was "approved" and modified it by removing bath from first floor bath to match my intentions. Came up with all sorts of monsters.

In the original drawing I was using a t for the horizontal lav to sink inlet. The shower drain is less than three feet from the new vent stack. I can run that by itself to a wye to connect it without combining them. The stack would qualify as the vent for the shower since it is so close.
 
Last edited:

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; The stack would qualify as the vent for the shower since it is so close.

NOT NECESSARILY. That is like saying that milk will not spoil if it is on the table close to the refrigerator. IF the shower's Y is between the vent and the toilet, then the stack will NOT, nor can it, be the shower's vent.
 

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
quote; The stack would qualify as the vent for the shower since it is so close.

NOT NECESSARILY. That is like saying that milk will not spoil if it is on the table close to the refrigerator. IF the shower's Y is between the vent and the toilet, then the stack will NOT, nor can it, be the shower's vent.

Are you meaning that if the shower's Y is on the horizontal between the WC and the vent it would need its own vent?

What I meant was I would go directly to the stack with its own sani-T rather than combine with the horizontal line from the WC/lav. Either stack two sani-T fittings vertically or use a sani-T hub (which I do not know if it is ok and asked about it in another thread). sanitary T_4871.jpg

It is mightily difficult to tie in the lav vent to the 3 inch stack in the attic but simpler just to have another roof penetration instead. How the shower branch connects and vents is what is left to figure out. Use sani-T hub, two vertical sani-T's or ? Without the shower the second floor plumbing looks like this so far. The shower is 90 degrees from the direction the WC comes in (hence the 3x3x3x2 hub thought).
upper bath redrawn copy.jpg
 

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
Shower connection options?

Options:
1.Use a combo sani-T hub 3x3x3x2 (would simplify things). Stack acts as vent for the shower.
2.Use a vented branch to a 3x3x2 sani-t. Venting required for the drop to get below the wc connecting sani-T.
3. Connect shower to lav waste via a Y fitting and add 2" vent near connection to3" Y between WC and stack vent. (Tie into WC 2" vent or into stack on its own?)
First Option:
hub_shower connection.jpg
Second Option:
vented sani-T upper bath.jpg
Third Option:
third option.jpg
 
Last edited:

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
I don't know how much "flexbility" you have as far as the pipe installation goes, but if it could be done, I would install the 3" stack at the lavatory with the 3x3x3x2 tee below it. Run the shower into the side, "offset" the toilet to its required location, and use a 3x1 1/2" tee for the sink. The way you have it drawn, however, NONE of the installations need the 2" vent at the toilet. Third option, neither the 2" for the toilet, nor that "cosmetic" vent on the sink/shower drain is necessary. There could be other possible "easier" layouts, if we knew the floor plan and fixture locations, or if you have a great deal of latitude on where the fixtures will be located, which seems to be case according to your various drawings.
 

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
Project photos for reference

The projects are in the garage and the bonus room above the garage utilizing a dormer area for a shower. The proposed 3" stack location is firm. The space above the stack in the kneewall is 50 inches tall. I can route it up the rafters to exit above the dormer valley. It lines up with vertically with the proposed bathroom wall below and the route to the basement to tie into CI stack. Nothing is framed on either floor, hence some flexibility. The hole through the poured concrete foundation on the first floor has been cut to access the CI stack in the basement.

Here are some pics for reference.

Bath floor plan area.jpgsecond floor bath plan.jpgView attachment 18499Bonus Room Floor Plan.jpg
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
Something like this works if you run 2" to the lav for the wet vent.
A wet vent minimum size is 2" on the wet portion.

The other drawing where you vent the shower by itself is good too.
It looks like you are learning. These latest drawings are head and shoulder better than the first one.
 

Attachments

  • both-levels.jpg
    both-levels.jpg
    39 KB · Views: 7,999
Last edited:

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
Thanks for pointing out the increase to 2" vent from the lav for the wet vent. As indicated by hj I would simplify the design and remove the 2" for the toilet and the "cosmetic" vent on the sink/shower drain, also.

Does the venting on the first floor look good?
 

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
I tweaked the drawing.

Thanks! I see you kept the 2" vent on the WC on the second floor (hj indicated it was uneccessary but both of you do not always agree). I can easily keep it. Does the first floor require adding similar venting at the WC or is the wet vent from the sink adequate?

Note: I also have planned a cleanout on the bottom of the vertical stack even though it is not indicated on the drawing.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Use the side inlet tee for the toilet and shower, (without ANY individual vents), then run the sink to the separate Y installed below it.
 
Last edited:

tireiron

New Member
Messages
23
Reaction score
0
Points
1
Location
MN
Use the side inlet tee for the toilet and shower, (without ANY individual vents), then run the sink to the separate Y installed below it.

I will use the side inlet tee as that is a very short run for the shower and simple. Is there an argument for running the sink waste to a sani-T vs the wye connection after the WC? Maybe as a "better" plan to isolate the WC? I think using the wye on the WC seems simpler to plumb.
Lav to wye vs to sani-T.jpg
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Either way is suitable. Lav to Y the stack is the vent for the shower and the lav is the wet vent for the toilet. Lav to T, the stack is the vent for the shower and the toilet and the sink has its own vent.
 