Shouldn't Light Fixtures Have Bare Grounding Wire Connected?

Users who are viewing this thread

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
You don’t have to run a wire all the way out to the ground rod to take a measurement. All you need to do if read the continuity of the green or bare and the white in the fixture.

In the service equipment the neutral (white), the equipment grounding (green or bare), the metal enclosure, and the ground rod will bond together so there is no need for the zip cord all the way back to the rod.
The path that you were reading was from the meter through the zip cord to the rod up the grounding electrode conductor to the neutral in the service back down the neutral to the meter.

All the rod does is the following;
250.4(A) Grounded Systems.
(1) Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.


As you can see the only purpose of the rod is incase lightning strikes or should there be a surge of voltage due to the switching of grids, should the conductors on top of the pole break due to ice or wind and fall down on the ones underneath and to keep the voltage of earth’s magnetic field and the voltage on the neutral conductors the same (stabilize).
 

DavidSeon

Member
Messages
47
Reaction score
0
Points
6
Location
MS Gulf Coast
You don’t have to run a wire all the way out to the ground rod to take a measurement. All you need to do if read the continuity of the green or bare and the white in the fixture.

Yeah, I kind of figured that. I did first verify continuity between the bare grounding and neutral conductors at the fixture as DonL suggested. I think I just got paranoid after finding so many fixture grounding wires hanging loose that I was afraid maybe they could have left things hanging loose in the main panel. In my simple mind I thought I was just making sure everything was properly bonded to the rod and really at earth ground.

I just can't get my brain around the principles of ground vs neutral in building wiring. I don't understand, if they both have the exact same continuous path back to each other and to earth ground, and apparently even back to the power company, what purpose the additional bare conductor has. Why do we care which of the two "ground" conductors the electrons use; I know this is wrong but to me, it seems like you could just use the neutral for grounding fixture housings and do away with the grounding conductor.

I guess that's just one of the reasons you're a pro and I'm NOT :)

Thanks again to everyone who replied.
Dave
 

Big2bird

IBEW Electrician
Messages
141
Reaction score
0
Points
16
Location
Anaheim, Ca.
Yeah, I kind of figured that. I did first verify continuity between the bare grounding and neutral conductors at the fixture as DonL suggested. I think I just got paranoid after finding so many fixture grounding wires hanging loose that I was afraid maybe they could have left things hanging loose in the main panel. In my simple mind I thought I was just making sure everything was properly bonded to the rod and really at earth ground.

I just can't get my brain around the principles of ground vs neutral in building wiring. I don't understand, if they both have the exact same continuous path back to each other and to earth ground, and apparently even back to the power company, what purpose the additional bare conductor has. Why do we care which of the two "ground" conductors the electrons use; I know this is wrong but to me, it seems like you could just use the neutral for grounding fixture housings and do away with the grounding conductor.

I guess that's just one of the reasons you're a pro and I'm NOT :)

Thanks again to everyone who replied.
Dave

Oversimplified, a nuetral is a current carrying conductor that "happens" to be at ground potential.
A ground conductors sole purpose is to bond all the metal parts, and to carry any fault current.
Even though they are at the same potential, they have differnent distinct "chores."
IF the nuetral was NOT at ground potential, and you looked at it as a hot wire, you would not be confused.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
I just can't get my brain around the principles of ground vs neutral in building wiring. I don't understand, if they both have the exact same continuous path back to each other and to earth ground, and apparently even back to the power company, what purpose the additional bare conductor has. Why do we care which of the two "ground" conductors the electrons use; I know this is wrong but to me, it seems like you could just use the neutral for grounding fixture housings and do away with the grounding conductor.

I guess that's just one of the reasons you're a pro and I'm NOT :)

Thanks again to everyone who replied.
Dave

Once a conductor is carrying current, then it becomes a load...meaning it has resistance and Ohm's law kicks in. The voltage at the source of the current will be I x R. A point in the neutral system can conceivably have several volts potential, with respect to earth ground. IF that point were tied to the bare ground wire, then the metal cabinet of your refrigrator, microwave, maybe even your shower head...whatever, would be at that potential...which is potentially dangerous.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
All of the current that goes out on the hot must return through the neutral. The ground wire should never be designed to carry current - it is there for protection as a safety backup and, if there were a short, to cause the breaker or fuse to trip. Ground would normally only carry current when there is some soft of fault.
 

DavidSeon

Member
Messages
47
Reaction score
0
Points
6
Location
MS Gulf Coast
Once a conductor is carrying current, then it becomes a load...meaning it has resistance and Ohm's law kicks in. The voltage at the source of the current will be I x R. A point in the neutral system can conceivably have several volts potential, with respect to earth ground. IF that point were tied to the bare ground wire, then the metal cabinet of your refrigrator, microwave, maybe even your shower head...whatever, would be at that potential...which is potentially dangerous.

I think that's the part I was missing. With electronic equipment I slipped into the habit of thinking of paths to chassis ground as dead shorts because, except with RF, the very small resistance/impedance can be ignored. So I was thinking of the neutral the same way; ie, if one end of the neutral is at 0 volts (relative to earth) at the panel, then the other end of that big copper wire was at 0 volts, too. Obviously, since the neutral carries current, that's not possible. It's not nice to forget Ohm's Law.

Thanks to everyone for your patience.
Dave
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Once a conductor is carrying current, then it becomes a load...meaning it has resistance and Ohm's law kicks in. The voltage at the source of the current will be I x R. A point in the neutral system can conceivably have several volts potential, with respect to earth ground. IF that point were tied to the bare ground wire, then the metal cabinet of your refrigrator, microwave, maybe even your shower head...whatever, would be at that potential...which is potentially dangerous.


"The voltage at the source of the current will be I x R."

If there is much R at the Source then something is wrong.

R should only come into play on the wire feeding the circuit, At its end destination point.


Jimbo is correct , but the wording could be a bit confusing. I get confused easy.
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Yes, what I was missing was a possible 15A across only 0.3 ohms at 4.5 volts is still 15A :eek:


That is not to bad of a voltage drop, depending on the wire length.

You just need to make sure the wire does not over heat.

When the wire gets hot, or over rated then it is best to use a bigger conductor. Voltage drop makes heat, somewhere.


If the source Voltage is low then a bigger wire will not help.

A better feed from the source current could help, but only if the power is available at its input.
 