Replace all Wiring that was Stolen any great suggestion???????????

Users who are viewing this thread

Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
I also run 12 for it all,except greater than 20 amps. Of course ,My work is repair n remodels, not track housing.

I do almost only repair and remodel. On the occasions that I do a full re-wire to get rid of old rag wire and to improve circuits (in conduit) I do as much as I can in 14 ga. There is a significant price differential as well, to my eye.

Obviously, if you are extending a circuit, you just match wire gauge to the protection existing.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
There are many misinformed people out there that think a 20 amp circuit is better than a 15 amp circuit for general purpose circuits.

Let’s look at this from a logical stand point. The cords that come on appliances used on general purpose circuits such as TVs, DVD players, lamps, ect… will be either a 16 or 18 gauge conductor. These cords have an ampacity of 7 and 10 amps respectively.
Using a 20 amp circuit to supply these appliances will allow at least 600 more watts of heat to travel through these cords in the event of a failure. This heat will most certainly cause more damage to the insulation than a circuit of lesser value.

Sometimes we think we are doing something that is better when in reality what we are doing is causing more problems. If we look at the owner’s manuals of some of these appliances we will find that plugging them into a 20 amp circuits is beyond the recommendations of the manufacturer.

What we seem to forget is that the breaker or fuse is there to protect the conductors not the appliance being plugged into the receptacle. Should a 15 amp circuit be overloaded the worst thing that will happen is the overcurrent device open but when we start installing a 20 amp overcurrent device on circuits that have cords that are rated at only 7 to 10 amps then we are causing problems especially if we are using such things as dollar store extension cords or plug strips.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
IF you do NOT "bash" the box out, but rather cut it out, then a "remodel box" should fit the opening and you have enough room to work the wires before installing the new box, meaning that there should be very little drywall repair to do. Connect the ends of all pairs of the cut wires together before going down into the room, then you can test all the wires at one time saving multiple trips into the attic.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
IF you do NOT "bash" the box out, but rather cut it out, then a "remodel box" should fit the opening and you have enough room to work the wires before installing the new box, meaning that there should be very little drywall repair to do. Connect the ends of all pairs of the cut wires together before going down into the room, then you can test all the wires at one time saving multiple trips into the attic.

Hmmmm. I like this. It depends a lot on what sort of boxes were used. Metal boxes with screw-down strain reliefs would be less amenable to this approach than plastic.

I don't know if I would trust remodel boxes with flip out lugs for receptacles, if the hole in the wall has been banged around a bit. If I did install them, and they were going in next to a stud, I'd think about drilling a couple of small holes and running some screws into the stud, if that would not cant the box around.

Anyway you count it, the OP has a mess on his hands, and would be well advised to have a relatively competent assistant on hand.

Hell, my daughter at age 6 helped me pull #2 thru some conduit that passed under a walkway between the house and garage. Ten years later she is almost less useful....
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
The cords that come on appliances used on general purpose circuits such as TVs, DVD players, lamps, ect… will be either a 16 or 18 gauge conductor. These cords have an ampacity of 7 and 10 amps respectively.
Using a 20 amp circuit to supply these appliances will allow at least 600 more watts of heat to travel through these cords in the event of a failure. This heat will most certainly cause more damage to the insulation than a circuit of lesser value.

Good points, frankly was not at the front of my mind.

For me the fact that is lots easier to work with 14ga and it demands less space in boxes and that it costs less motivates me to use it as much as I can.

Just like I try to use the smallest legitimate wire nut, in order to fill the boxes less.
 
Last edited by a moderator:

Toolaholic

General Contractor Carpenter
Messages
894
Reaction score
6
Points
18
Location
Marin Co. Ca.
There are many misinformed people out there that think a 20 amp circuit is better than a 15 amp circuit for general purpose circuits.

Let’s look at this from a logical stand point. The cords that come on appliances used on general purpose circuits such as TVs, DVD players, lamps, ect… will be either a 16 or 18 gauge conductor. These cords have an ampacity of 7 and 10 amps respectively.
Using a 20 amp circuit to supply these appliances will allow at least 600 more watts of heat to travel through these cords in the event of a failure. This heat will most certainly cause more damage to the insulation than a circuit of lesser value.

Sometimes we think we are doing something that is better when in reality what we are doing is causing more problems. If we look at the owner’s manuals of some of these appliances we will find that plugging them into a 20 amp circuits is beyond the recommendations of the manufacturer.

What we seem to forget is that the breaker or fuse is there to protect the conductors not the appliance being plugged into the receptacle. Should a 15 amp circuit be overloaded the worst thing that will happen is the overcurrent device open but when we start installing a 20 amp overcurrent device on circuits that have cords that are rated at only 7 to 10 amps then we are causing problems especially if we are using such things as dollar store extension cords or plug strips.
Same 18 Ga. cord can be plugged into a 20 amp plug ! My logical stand point.
 

Chad Schloss

Member
Messages
327
Reaction score
0
Points
16
Location
USA
"If we look at the owner’s manuals of some of these appliances we will find that plugging them into a 20 amp circuits is beyond the recommendations of the manufacturer."

the appliance does not care what is it plugged into, as long as the prongs fit.. as you stated, the OCP for the wire in the wall is the 20a breaker at the panel. as for the 18 ga cord, that is up to the appliance to be fused. 20a vs 15a, it's still going to blow that fuse in the radio/tv/whatever. i guess i don't see your point. if 12 ga was 'incorrect' to use, it would not be able to be used for such a purpose, don't you think? our current house is wired the same way ( i didn't wire it, bought it like that in 2005, new build) and have had zero issues, except from where the 'rockers' got carried away with a rotozip and hit a wire i had to fix.

i just rewired my rental house. i used 12 ga in most receps, and 14ga for all lighting, outlets separate from lighting. if you are wiring a living room with 10 receps, with your tv/stereo, table lights, etc and then run a something like a vacuum, it gives you what, 600 more watts to play with? yeah, i'll take that, rather than string another dedicated line for a living room circuit.
 
Last edited:
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
Cif you are wiring a living room with 10 receps said:
Holy crap! Ten receptacles in one living room? You have the Queen of England as a client?

It is a large living room indeed that needs more than six receptacles by code.

I suppose you could be running your monster stereo at full whack so that you can hear it over the vacuum cleaner and then somehow, with a massive flat screen in the room running a vampire load, and then trip the breaker.

That is one huge living room.
 

Toolaholic

General Contractor Carpenter
Messages
894
Reaction score
6
Points
18
Location
Marin Co. Ca.
Well said, On My using 12 Ga. in remodeling came from a retired Master Elec. in S.F.He was a German that polished the Ice Cubes ! Nuts on .
 

Drick

In the Trades
Messages
460
Reaction score
19
Points
18
IF you do NOT "bash" the box out, but rather cut it out, then a "remodel box" should fit the opening and you have enough room to work the wires before installing the new box, meaning that there should be very little drywall repair to do. Connect the ends of all pairs of the cut wires together before going down into the room, then you can test all the wires at one time saving multiple trips into the attic.

I work with mostly fiberglass boxes. The easiest thing to do is bash the fiberglass box apart and pull the remaining nails. If your dealing with plastic big box store quality boxes its easier to use a sawz-all and carefully cut the nails and then pull the box. Also they make old work boxes that can be screwed to a stud from inside the box so you don't have to rely on the tabs. They are a bit more expensive but worth it if you are up against a stud.

-rick
 

Chad Schloss

Member
Messages
327
Reaction score
0
Points
16
Location
USA
"Holy crap! Ten receptacles in one living room?"

this was a house from the 50's. it is a small ranch, and had i think 4 outlets. if you don't want power strips laying around on your floor, you add outlets where you want them. I also added a few more receps in places where people may not use them, but some would, like below a window in the foyer area. some people light up the windows at the holidays with lights/candleabras, etc, so i put one there, another near the end of the room to plug in a vacuum or floor cleaner, etc so you wouldn't have to move a piece of furniture to access a recep. i used 10 as a round figure, i actually think i have 7, with two being on ganged together for the tv area in the corner on one wall, and on the other wall another near those for more a/v equipment.

at our house right now, i have a single gang outlet with one of those things you insert into the single gang outlet and you get 6 outlets out, and i still need another outlet. i hate power strips. i came home from vacation last time and i had one plugged into a lamp, just to make the cord reach, that's all that was plugged into it, and i came home to the power strip smelling like it was on fire. sure enough, i took it apart, the MOV's inside had melted and melted some of the plastic. I have a whole- home surge protector, so i think this one was just garbage. i refuse to use them anymore.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
"If we look at the owner’s manuals of some of these appliances we will find that plugging them into a 20 amp circuits is beyond the recommendations of the manufacturer."

the appliance does not care what is it plugged into, as long as the prongs fit.. as you stated, the OCP for the wire in the wall is the 20a breaker at the panel. as for the 18 ga cord, that is up to the appliance to be fused. 20a vs 15a, it's still going to blow that fuse in the radio/tv/whatever.
Section 110.3(B) of the NEC states that any appliance of piece of equipment must be installed by the instructions so to install an appliance on a 20 ampere circuit when the manual states for it to be installed on a 15 amp circuit is a code violation.
As far as the appliance itself one could use jumpers from the meter base and the appliance wouldn’t care as long as it had current flow. The overcurrent device is installed to protect the conductors not the appliance so it wouldn’t care if it was wired straight to the transformer. Believe it or not but that surge protector or plug strip with the radio/tv/whatever plugged into it don’t care either but the owner might when the insulation starts smoking. These devices are one of the leading causes of fire in our homes today so why put them to the test?

i guess i don't see your point. if 12 ga was 'incorrect' to use, it would not be able to be used for such a purpose, don't you think? our current house is wired the same way ( i didn't wire it, bought it like that in 2005, new build) and have had zero issues, except from where the 'rockers' got carried away with a rotozip and hit a wire i had to fix.
It would only by a violation if there was something in one of the manuals for one of the appliances that called for a 15 amp circuit but common sense plays a role here also. When using things like extension cords and plug strips the fact that 18 gauge conductors are only good for 7 amps and 16 gauge conductors are only good for 10 amps why would someone want to plug one into a circuit that has 25% more heat energy available? Could it be that they believe that that 20 amp circuit is somehow better?

" i just rewired my rental house. i used 12 ga in most receps, and 14ga for all lighting, outlets separate from lighting. if you are wiring a living room with 10 receps, with your tv/stereo, table lights, etc and then run a something like a vacuum, it gives you what, 600 more watts to play with? yeah, i'll take that, rather than string another dedicated line for a living room circuit.
What role does 10 receptacles play in this discussion? This is a dwelling unit not a commercial or industrial installation where the load is calculated on the device but is instead calculated on the square feet.
In commercial and industrial installations all duplex receptacles are to be calculated at 180 volt amperes each. The reason for this is that one will not be installed unless it is planned on being used. In a dwelling unit we must install receptacles per 210.52 at regular intervals. These devices are sometimes never used so there is no need to figure them at 180 volt amperes each but instead at 3 volt amperes per square foot.

All of this thinking of 20 ampere circuits for dwelling receptacles and separating the lights from the receptacles comes from commercial and industrial installations. The adage was passed from the commercial trade to the residential trade through commercial electricians that only did commercial and industrial installations then one day doing a dwelling and using what they had learned.


A quick look at 210.21 through 210.23 one will learn that if a 15 amp receptacle is being installed then the maximum load that can be plugged into it is 12 amps and it doesn’t matter if it is a 15 or 20 overcurrent device.
So what does one gain by installing 20 amp circuits and not installing 20 receptacles? Nothing. What does one gain by installing 20 amp circuits and 20 amp receptacles? The cost of the 20 amp receptacles are twice that of 15 amp receptacles. Their only gain is more cost and a waste of our natural resources.

So is the 20 amp circuit for a dwelling unit better than a 15 amp circuit? It depends on who you talk with. Those that I talk with say no the 20 amp circuit is more dangerous than a 15 amp circuit. These are some of the greatest minds in the electrical trade not some master electrician that has retired nor is it some unfounded wives tale that was started many years ago. It is those who are charged with writing, testing, and researching the codes and installations for electrical energy.
 

Toolaholic

General Contractor Carpenter
Messages
894
Reaction score
6
Points
18
Location
Marin Co. Ca.
Living in the real world, teens n Moms will be plugging "WHAT EVER IN WHERE EVER" Most teens don't don't have the NEC on the nite table !
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
It is not a matter of Mom or teens or even what they are plugging into a receptacle. The NEC is directed toward the installer and the code enforcement official that will be doing the inspection not for Moms and teens that will be plugging things in.

The adage that more is better or a 20 amp circuit is better than a 15 amp circuit encompasses a lot more than Moms and teens. It even encompasses more than the NEC. It has more to do with the cords that Moms and teens are plugging in than anything else.

One does not have to be a rocket scientist to know that in a fault situation it will take longer to open a 20 amp device than a 15 amp device. If this is a high impedance fault such as cracking in the cord insulation then it is possible that neither device will open but it is common sense that says the 15 amp device will open quicker than a 20 amp device.

If we are going to play with the bigger is better aspect why not just install everything on a 30 amp circuit. Now we can watch TV, listen to the radio and vacuum the floors all at the same time without worrying about the breaker tripping. Mom and the teens could plug in whatever their hearts pleases.

Edited to add:
On a side note let me say that there is no violation in installing 20 ampere general purpose branch circuits but common sense will say those things that I have pointed out.
It is not cost effective to install 20 amp general purpose circuits and the comments that it is better is not true but the opposite. There is no advantage in installing the 20 amp circuits but it does cause dangers to lurk.
 
Last edited:
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
What role does 10 receptacles play in this discussion? This is a dwelling unit not a commercial or industrial installation where the load is calculated on the device but is instead calculated on the square feet.

This is essentially my point regarding having more receptacles in a living room than is required by code, just to appreciate where one wants outlets and to avoid extension cords. Avoiding extension cords is a good idea. But in a residence one calculates load based on sq ft. If one is starting from scratch one can certainly put in an extra general lighting circuit to lessen the load on each of the general lighting circuits, but one should start knowing what the minimum requirement is before gilding the lilly.

I wired my addition while the General handled all the rest. My master bedroom is about 15' x 14'. There are several doors, which break up the walls for figuring where the outlets need to be. But I have nearly twice as many outlets as would minimally be required. The bed could be placed against either of two walls. I could have used one outlet in either case, but the receptacle would have ended up behind the bed, which is a thing I avoid as best as I can. Customers pretty quickly see the value of not having the plugs buried behind the bed! There are two other outlets in the room that are only there because it is more convenient, and avoids extension cords.

I don't charge myself much for my work......

But I certainly did not need to wire them for 20 amps. There is a TV and some lights and a clock radio.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Just to let you know that like most things, there are differing schools of thought. I am pretty sure that the electrical code in Canada does NOT allow a 15 amp device on a 20 amp breaker. So they evaluated the whole situation and came down on the other side of the argument
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
As long as the wire is sized properly, I do not see the big deal.

Most if not all appliances will have a fail-safe device built in.

Even a power strip / surge protector will have a 15 amp or normally less protection device built in.


The breaker in the panel will Rarely blow when a appliance fails, or a kid sticks a knife into the outlet or toaster.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I have yet to see an appliance that had overcurrent device installed in it such as TV radio ect......
Have you got a wiring digram that shows this?
 

Chad Schloss

Member
Messages
327
Reaction score
0
Points
16
Location
USA
I have yet to see an appliance that had overcurrent device installed in it such as TV radio ect......
Have you got a wiring digram that shows this?

i used to work for sony, repairing electronics. there are fuses and sometimes even circuit breakers in most everything, from tv's to little cd players to your grandson's playstation.
 