Horizontal Washer Drain AFTER Standpipe 3 iinch??????

Users who are viewing this thread

Hammerlane

Member
Messages
275
Reaction score
13
Points
16
Location
Ohio
I have another thread on here about how to plumb a washer and utility sink into an existing 4" stack. My plan was to run 2" horizontally to pick up the laundry sink and washer after tying into the stack.

I talked with our local inspector here in Ohio and he said that any horizontal run to the stack after the washer standpipe has to be at least 3". He said the standpipe can be 2" but the horizontal run to the stack has to be at least 3"

I checked into the Ohio Administrative Code » 4101:3 Board of Building Standards: Ohio Plumbing Code » Chapter 4101:3-4 Fittings and this is what it states for clothes washers:



AUTOMATIC CLOTHES WASHERS

406.3 Waste connection. The waste from an automatic clothes washer shall discharge through an air break into a standpipe in accordance with Section 802.4 or into a laundry sink. The trap and fixture drain for an automatic clothes washer standpipe shall be a minimum of 2 inches (51 mm) in diameter. The automatic clothes washer fixture drain shall connect to a branch drain or drainage stack a minimum of 3 inches (76 mm) in diameter. Automatic clothes washers that discharge by gravity shall be permitted to drain to a waste receptor or an approved trench drain.

So I wonder if running the 2" horizontally after the standpipe into the 4" stack will satisfy this code since the code says, "fixture drain shall connect to a branch drain or drainage stack a minimum of 3 inches (76 mm) in diameter."

The "or" part gets me. Looks like you have to connect into a branch drain OR stack of at least 3". well I'll be connecting into a 4" stack. I can't imaging I would need 3" for the run to the stack. How do you interpret this?


In the photo disreagrd the fittings they are not final yet. Just address the "green horizontal" run the will pick up the standpipe and sink then terminate into the stack.

Thanks.
 

Attachments

  • smaller pic green branch 3 line--laundry stub shown.jpg
    smaller pic green branch 3 line--laundry stub shown.jpg
    40 KB · Views: 1,728
Last edited:

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
... a branch drain or drainage stack a minimum of 3 inches (76 mm) in diameter.

The "or" part gets me. Looks like you have to connect into a branch drain OR stack of at least 3" ...
Yes ...

... a branch drain ... a minimum of 3 inches (76 mm) in diameter.
... a ... stack a minimum of 3 inches (76 mm) in diameter.

If the branch drain did not have to be 3", the text would likely convey something like this:

... either into a branch drain or into a stack, and then the stack would have to be at least 3".

The poor wording in the code might seem ambiguous, but your inspector seems to understand what is meant.
 
Last edited:

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
I can tell you how it is here (code for this is written like Ohio).

In my case, I was able to do 2" standpipe, trap, and short run to stack. At the stack, I had 3" going down and 2" vent going up. No problem.

What you have to look at is the definition of those terms:

Fixture Drain: The drain from the trap of a fixture to a junction with any other pipe. (so from the trap to your wye used for the vent)

Branch: Any part of the piping system except a riser, main or stack

To me, you could go 2" up to your vent and will need to go 3" at/after that point.

Yes, you will need the vent as the run looks too long otherwise (limit is typically 6'-8' for 2" pipe) and that stack is getting a dischange from above, so it couldn't be used as a vent anyway (if you were closer).

Does that smaller line at the top of the stack drain anything from above? If so, you can't use it as a vent.


However, what we think the code says doesn't matter. You can try to make a case for using 2" up to where you connect the vent, but all that matters is what the inspector thinks the code says. It is his job to interpret the code and enforce it. If he thinks you need 3" after the trap, then you'll need 3" after the trap (if you want to pass).
 

Hammerlane

Member
Messages
275
Reaction score
13
Points
16
Location
Ohio
The 4" stack in the photo is servicing only 2 floor drains in my garage. You can see about 7 feet up on the stack where the 4" San-T ties in to pick up the floor drains. On top of this 4" San-T is a bushing for the 2". The 2" serves as a vent. This is the vent I was planning on tieing into for the laundry sink / washer standpipe set-up. No other fixtures in the house drain into this stack above where you see the San-T picking up the garage floor drains

See updated photo.
 

Attachments

  • smaller pic green branch 3 line--laundry stub shown--no vent above sant.jpg
    smaller pic green branch 3 line--laundry stub shown--no vent above sant.jpg
    42.6 KB · Views: 3,869

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
It is a question of semantics and interpretation. The code says "trap AND fixture drain shall be 2", but it does NOT specify what is meant by "fixture drain" or how far it can go before it has to be increased to 3". Normally, the washer drain "system" would be an integral package and then that package would connect to a 3" branch/riser drain. To this date, I have NEVER had to run 3" to a washer drain connection, but the washer drains DO eventually connect to a 3" or 4" drain line.

As for #3, "is this vent needed" the answer would be yes, but you CANNOT connect it to the system at the ceiling where you show it, unless that point is 6" above the garage floor and the inspector approves it.
 
Last edited:

Kevin-NC1

New Member
Messages
4
Reaction score
0
Points
1
Location
North Carolina
I have a question about draining a clothes washer into a laundry sink per the code above, which looks very much like the code where I live.

My question is this: If there is no standpipe for the clothes washer and the washer drains directly into a laundry sink would the requirement for a 3" horizontal line still be valid (following the laundry sink), or does the requirement for a 3" horizontal run "e.g. automatic clothes washer fixture drain shall connect to a branch drain or drainage stack a minimum of 3 inches" apply only if a typical laundry 2" standpipe/P-trap is used as the drain for the clothes washer?
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks