Mike2187

New Member
Messages
9
Reaction score
0
Points
0
Location
Maryland
I am in the midst of remodeling my bathroom and exposed the plumbing. I wanted to replace the old lead P trap. I called in a plumber and he said that a new p trap would poke through the hole of the ceiling downstairs (2nd floor bath remodel). The clearance is too tight. The plumber is well familiar with these Levitt homes.

I did some research on waterless p traps and found the HepVo.

https://drainmaster.com/main/2012/02/01/hepvo-waterless-p-trap-how-big-is-it/

It will fit in the adjacent bay and when I called the company, the rep said that it can be mounted as far as 3 feet away from the drain. I less than half that. However a vent pipe is posing a problem for placement.

mike2187-01.jpg


Water flows from left to right. Top pipe is vent.

I did this:

mike2187-02.jpg


The HepVo will be mounted just left of the tee.
Will this work? Should I make the tee a wye? Does the tee have to be under the vent at all times?

Thanks in advance
 
Last edited by a moderator:

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
Wow...

Now I've seen everything.

What does your inspector say when you tell him you don't think you need a proper trap?
 

Mike2187

New Member
Messages
9
Reaction score
0
Points
0
Location
Maryland
Thank you for your helpful post.

The waterless trap is slated for approval in 2015. Over 7 million homes in Europe currently us them. Here are three Brits testing the back pressure on the thing.


I called the company and specifically asked about inspectors. He advised that technology is surpassing code and plumbers hate change. He further advised that it will pass inspection but you have to meet with the inspector and show him the device. They will pass it under their exception or miscellaneous clause. Not too sure of the word he used at the moment.

I just need to know if it's vented wrong.

Also they installed 1800 of these things at the newly built world cup soccer stadium in south Africa.
 
Last edited by a moderator:

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
Thank you for your helpful post.

The waterless trap is slated for approval in 2015. Over 7 million homes in Europe currently us them. Here are three Brits testing the back pressure on the thing.

I called the company and specifically asked about inspectors. He advised that technology is surpassing code and plumbers hate change. He further advised that it will pass inspection but you have to meet with the inspector and show him the device. They will pass it under their exception or miscellaneous clause. Not too sure of the word he used at the moment.

I just need to know if it's vented wrong.

Also they installed 1800 of these things at the newly built world cup soccer stadium in south Africa.

So the salesman did his job...?
 
Last edited by a moderator:

Jerome2877

In the Trades
Messages
397
Reaction score
2
Points
18
Location
Vancouver Island , BC
That product is for RV's, it will not pass any North American code for use in a house. With an RV your not dealing with dangerous sewer gas, just bad smell from a holding tank. What happens when your drain clogs? A little hair and it wll clog and probably cause the device to fail.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
RVs do NOT have any plumbing codes so you can use whatever you want to in them. This thing would NEVER pass any code requirement, and I do not know what would be magical about the year 2015 that it would suddenly be code compliant then. It has a "diaphragm" inside it which will create a restriction, which is one code violation. The trap's "seal" depends on the diaphragm opening to let water out and closing to keep air out the other way, which is code violation #2. It MUST be in an accessible location to replace the diaphragm when it hardens from age and no longer flexes, which means it CANNOT be installed under floor or in any other closed area. If you could get that thing approved by ANY city or inspector, you might as well just use a check valve which does the same thing, but does it more reliably. Additionally, it is "tubing size" which means you would have to use slip joint fittings between the tub and the "trap", which would NOT be one of your greatest ideas. Your real problem is that you are eliminating a brass, NOT lead, "P" trap. A brass trap is a lot "shorter" than one of any other material.
 
Last edited:

Mike2187

New Member
Messages
9
Reaction score
0
Points
0
Location
Maryland
It is a lead p trap I am replacing

lead-p-trap-01.jpg


It will be accessible through the ceiling of the first floor (second floor bathroom).

The slip joint does concern me however. Do they even make brass p traps anymore? I also considered raising the floor of the bathroom but then I would have a ridiculously canted marble transfer piece between hall and bathroom.
 
Last edited by a moderator:

Mike2187

New Member
Messages
9
Reaction score
0
Points
0
Location
Maryland
It is a lead p trap I am replacing

lead-p-trap-01.jpg


It will be accessible through the ceiling of the first floor (second floor bathroom).

The slip joint does concern me however. Do they even make brass p traps anymore? I also considered raising the floor of the bathroom but then I would have a ridiculously canted marble transfer piece between hall and bathroom.

What about adding a sureseal? Is this a check valve?

http://www.thesureseal.com/
 
Last edited by a moderator:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
NO, NO, NO and NO is the answer to all the questions. If there is another question, the answer to that is also NO.

IAPMO will approve a ham sandwich if you pay them enough, but I cant imagine them approving that waterless trap. It will drain slowly, will clog almost immediately with the hair in a tub or lav drain. Ditto for the trap seal.
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
One of the hotels in Bellevue used self venting fittings in the cast iron piping of the building. When I stayed there a few years later, I could hear the tub trap being sucked dry.
I was not impressed.
And yet, somehow it had become code. I guess it worked when it was new, but then things start to gunk up and then they quit doing the job.
But then it's your bathroom, and if it quits doing the job, you can always replace it.
A normal p-trap costs very little, why would you spend more money for something mechanical that will fail over time?
The vent you installed should have been a wye fitting. Previously you had a backwards santee for venting. The trouble with copying old plumbing sometimes, is you have no idea if the previous installation met code the first time, and then there have been improvements over the years, fixing mistakes that old codes allowed.
 

Mike2187

New Member
Messages
9
Reaction score
0
Points
0
Location
Maryland
Thanks jimbo. Looks like I'll half to bite it. Ugh. How fitting that a bullet usually is brass and copper.

Thanks Terry for answering my venting question.
 

Mike2187

New Member
Messages
9
Reaction score
0
Points
0
Location
Maryland
P trap will have to poke through ceiling. Maybe I'll have someone box out a section in ceiling. Idk
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Thanks jimbo. Looks like I'll half to bite it. Ugh. How fitting that a bullet usually is brass and copper.

Thanks Terry for answering my venting question.

It doesn't show well in the photo, but notice in 'properties' that this is a SILVER bullet!
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Get a brass "sweat P trap" and it will be almost the same dimensions as that lead trap. I cannot imagine someone, even then, using a lead trap with a copper drain system.
 

Mike2187

New Member
Messages
9
Reaction score
0
Points
0
Location
Maryland
I found a cast brass one on ****. I hope this will work.

mike2187-03.jpg
 
Last edited by a moderator:

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; One of the hotels in Bellevue used self venting fittings in the cast iron piping of the building.

I assume it was a So-Vent system. If the lead trap worked the brass one should also, especially a 1 1/2" one.
 