I have heard that I should not use pex between a shower valve and tub spout because of resistance. I will be using a 3/4" thermostatic valve with separate volume controls for the tub and multiple shower heads; all 3/4".

Having volume controls for everything including the tub, anyone see a problem using 3/4" PEx for everything and no copper as long as its all strapped down?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
You'll lose some of the volume capability of the valve if you use pex. Often, they specifically say not to use it to interconnect pieces. Using it as a supply also means you won't get the maximum volume you could have. in a traditional setup, using 1/2" pex, with a divertor spout, it will back up into the shower. Since most stub spouts are 1/2", using pex to it would be a problem. I'd use copper after the valve for all connections. This will also mean that you can anchor it well.
 

tomtbone

Member
Messages
31
Reaction score
0
Points
6
Location
tomtbone in Boston
Website
www.ottoplanet.net
I am not using a traditional setup however with a diverter. The tub spout is basically plumbed like another showerhead, it has its own volume control (on/off). I suppose I could always use 1/2" copper to go down to the tub spout, but I could also use Pex drop ear elbows screwed into 2x4's. and that would be just as solid right?
 

NHmaster3015

Master Plumber
Messages
833
Reaction score
2
Points
0
Location
The granite state
The reason for not using it between the valve and the spout is because the added restriction can force water up through the shower head when you are filling the tub. The mixing valve should have no effect one way or the other. If you don't mind the shower head dribbling than go for it.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
The issues you heard about involve using 1/2" PEX on a 1/2" shower valve. I suspect the same issue would apply to using 3/4" PEX on a 3/4" valve. Consider using copper for the drop to the spout. And remember in terms of your overall plan, that 3/4" PEX is more or less equivalent to 1/2" copper.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
You do NOT have the same dynamics in your design that a diverter spout would. ALL of your devices will have a positive shutoff valve in the line going to them so it makes no difference WHAT you use, or the size, to any of them, including the spout. A bigger issue, if the thermostatic valve has an on/off function would be that you should NEVER have all the volume control valves off at the same time. Even though the valve should have "check stops", you could leave the valve turned on, and stop the flow with the volume controls, which could create a "cross over/backflow" situation between the hot and cold systems.
 

tomtbone

Member
Messages
31
Reaction score
0
Points
6
Location
tomtbone in Boston
Website
www.ottoplanet.net
You do NOT have the same dynamics in your design that a diverter spout would. ALL of your devices will have a positive shutoff valve in the line going to them so it makes no difference WHAT you use, or the size, to any of them, including the spout. A bigger issue, if the thermostatic valve has an on/off function would be that you should NEVER have all the volume control valves off at the same time. Even though the valve should have "check stops", you could leave the valve turned on, and stop the flow with the volume controls, which could create a "cross over/backflow" situation between the hot and cold systems.
What I have is a Kohler Thermostatic valve, with no volume control built in. IT is meant to only control the temperature.
http://www.us.kohler.com/onlinecatalog/pdf/1041158_1.pdf
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Read the installation instructions very carefully. Many of them must have the water going INTO them turned off, i.e., not have the water OUT of them stopped. This is why most people use a multiport divertor valve rather than multiple stops. If it isn't obvious from the instructions (it may only be one line or word burried somewhere), I'd call the manufacturer's tech support line and specifically get their okay for your installation plan...
 

tomtbone

Member
Messages
31
Reaction score
0
Points
6
Location
tomtbone in Boston
Website
www.ottoplanet.net
This is what it says in the directions:

The K-669 and K-679 thermostatic mixing valves do not contain an integral volume control/shut-off valve. You must install a separate volume control/shut-off valve (K-671 or K-681)
downstream of any used valve outlet.

thermo.jpg
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks