OT: Efficieny of Boilers vs Heat Pumps

Users who are viewing this thread

Chefwong

Member
Messages
949
Reaction score
11
Points
18
Location
District of Columbia
OT: boiler gurus but I have a closed loop mixed system. Some Baseboards are cast iron and some are old school . I do know is CONSIDERBLY cheaper than electric out here in NYC but love to hear your thoughts.

I have a older Pennco Boiler in my 80-100 year old home.
Curious on your thoughts of efficiencies of the heat pumps in ductless systems vs. old school closed loop boiler/hot water systems

https://terrylove.com/forums/forumdisplay.php?13-HVAC-Heating-amp-Cooling
 

NHmaster3015

Master Plumber
Messages
833
Reaction score
2
Points
0
Location
The granite state
change the boiler. Either Buderus or Viesmann would be my to choices. Get outdoor re-set control with either. Leave the baseboard alone.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
What Wally said (but I like Triangle Tube & Peerless- there are MANY good modulating/condensing boilers out there.) Odds are, if you've upgraded the insulation & air tighness of the building in the past 80-100 years the boiler & radiation is oversized, and never ran better than 70% efficiency on it's best day, with an average AFUE under 60%. A properly sized modulating boiler will cut the heating fuel by at LEAST 25%, and 40% isn't unheard of, and 90%+ efficiency isn't out of the question.

Old-school cast iron radiation is good stuff- much nicer to live with than baseboard convectors or wheezy-breezy heat pumps with tepid-air output. But get a room-by-room heat loss analysis as step-1 with any heating system- your comfort & operating efficiency depend on it. MOST boilers in the northeast are oversized for the true loads, to the detriment of both. (Which is why modulating boilers are preferable- they can be tweaked for higher comfort, which usually means higher efficiency as well.)
 

Lightwave

New Member
Messages
98
Reaction score
0
Points
0
Location
Vancouver, BC
Curious on your thoughts of efficiencies of the heat pumps in ductless systems vs. old school closed loop boiler/hot water systems

There's really no contest. The best boiler setup will be no more than 90% efficient. A well designed heat pump will be at least %200 "efficient" in terms of heat generated from power consumed.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
There's really no contest. The best boiler setup will be no more than 90% efficient. A well designed heat pump will be at least %200 "efficient" in terms of heat generated from power consumed.

That's some pretty fuzzy thinking in the real world.

From % of fuel energy delivered to the load point of view a heat pump driven by a combustion-fueled electric grid needs to have a COP of 3 or greater to match a 90% efficient fossil-fired heating system. The average N. American fossil-fired plant sends ~65% of the fuel energy directly up the flue & cooling towers, and and another 6-10% gets eaten up in distribution losses, for a net ~25-30% fuel-to-load efficiency. Nuke fuel-to-load efficiencies are are even worse. The NYC the grid is powered with a preponderance of fossil & nuke plants. Combined-cycle gas plants run about 55-60% efficiency fuel/load though.

A "best boiler setup" with low-temp radiation (radiant floors or celings) can easily average in the ~95-96% range in a well designed system- 90% is the low end of where a mod-con runs, even on old-school radiation (if properly sized & optimized.)
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
WHAT is "considerably cheaper than electric" out there?
The practicality of a heat pump depends to a great deal on WHAT your temperature range is, and whether you would have to resort to "resistance" supplemental heat in the form of heat strips on the coldest days.
By ductless systems I assume you mean a forced hot air system, and that is a different animal than hot water systems, which by the way are ALL closed loop.
 