Any risks to merging two 3/4" copper water supplies? (using T fitting)

Users who are viewing this thread

CJ-8_Jim

New Member
Messages
3
Reaction score
0
Points
1
Location
Chicago Suburbs
I’m splicing in another water filter in parallel to existing filter (to double velocity).

Does anyone foresee any problems (performance or otherwise) with merging two ¾†copper water supplies into one using a “T†fitting?
That is, one supply will come into the “T†from the left and the other supply will come in from the bottom.

Thanks for your input.
Jim

It will roughly look like this when done:
 

Attachments

  • Water Filter plumbing.jpg
    Water Filter plumbing.jpg
    20.7 KB · Views: 509

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
What are you trying to filter out? Cartridge filters are generally bad news as they harbor the growth of bacteria and must be replaced constantly. A backwashing filter is almost always more appropriate. If you need more filtration, it's time to start finding out why rather than just adding more filters.
 

CJ-8_Jim

New Member
Messages
3
Reaction score
0
Points
1
Location
Chicago Suburbs
Still looking for an answer -- can anyone advise?

What are you trying to filter out? If you need more filtration, it's time to start finding out why rather than just adding more filters.
Sorry you are confused -- perhaps the diagram is not clear that I'm adding a filter in parallel. As you probably know, doing so does not increase filtration, but will increase velocity (which is my goal).

i don't use copper on well lines. You can do that if you want...
Why are you assuming the well is copper?

The house was built in 1969. The whole house is copper except the well.

Are you suggesting I hire a plumber like yourself to replace all the copper pipes in the house? Do you believe that is necessary? (Though it would be profitable for you.)
 

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
I see no problem except the the new filter will receive more flow that the current filter as there is a shorter path on both sides of the filter. To better balance, you could bring the feed between them with a tee and use an elbow for the new filter. Then do the same on the outlet side.

With the current layout, the new filter may need to be replaced before the other filter as it will be a greater % of the flow (difference may be small, though).
 

CJ-8_Jim

New Member
Messages
3
Reaction score
0
Points
1
Location
Chicago Suburbs
Thanks much. I was guessing that too -- maybe I'll just T them off evenly (but that's adding more right angles which impact flow).
 

Jastori

Member
Messages
122
Reaction score
0
Points
16
Location
Illinois
The restriction in flow due to the 3/4" T's will be negligible compared to the restriction from the filter itself. Balancing the piping on both sides is the ideal way to do it, although likely a minimal difference as well.
 
Last edited:

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
filter

There is almost NO advantage to piping it any differently than your original drawing. The flows will automatically balance themselves as one filter starts to accumulate more "debris" than the other.
 