Split 110v off a 230v branch circuit?

Users who are viewing this thread

JeffeVerde

Member
Messages
86
Reaction score
2
Points
8
Location
L.A.
Is it possible to split out a 110v branch from a 230v branch circuit? I'd like to put an exterior light and 15A receptacle near my A/C compressor, but it's a 120' run back to the panel, and access it difficult.

I've got a 230v/50A circuit supplying the A/C compressor and the compressor only requries 35A, so overloading the 50A circuit isn't an issue. The A/C circuit terminates in a fused disconnect box, and then a whip into the unit.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Not sure if this is legal, but would only be possible if they ran a neutral. If you only have two wires and ground, then no. If you have three wires plus ground, then yes. From neutral to one hot is 120vac. You'd get the same 120vac from one hot to ground, but that would not be code or safe
 

JeffeVerde

Member
Messages
86
Reaction score
2
Points
8
Location
L.A.
The 230v circuit is #6-3 w/ground. This will be inspected, so along with safety, code compliance is also important.
 
Last edited:

Arfeller

Member
Messages
88
Reaction score
3
Points
8
Location
Port Angeles, WA
So, if i understand correctly, you have a 6/3 + ground. So two (2) hots, one (1) neutral, and one (1) ground going to the compressor?

If you do have the neutral then splitting out a 110 v ciruit should not be a problem. However, you might run into problems with the fused box.

I had a fused box that would not support splitting a circuit like that so had to replace it with a subpanel. They are pretty cheap ~$35 at home depot + another ~$30 for breakers you might need.

I recently ran 2x #6 hot, 1x #8 neutral, and 1x #10 ground to a subpanel and have a 220v circuit and two 110 v circuits.

I'm not an electrician and am only speaking from DIY projects i have recently done.

So make sure and get comformation of this :)
 

Drick

In the Trades
Messages
460
Reaction score
19
Points
18
Remove your outdoor A/C disconnect and replace it with a small weatheproof subpanel. Add the proper sized 2 pole breaker for the A/C and then add a 20A single pole breaker for your outside outlet. The subpanel will act as a disconnect for the A/C so you will no longer need the disconnect.

-rick
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
230

VERY few air compressors have a neutral wire, since they do not have any 110/120 volt components. In addition, the circuit breaker is primarily to protect the wires, NOT just the appliance, so any wires connected to that circuit would have to be rated for 50 amps, which is a little large for a duplex receptacle.
 

Arfeller

Member
Messages
88
Reaction score
3
Points
8
Location
Port Angeles, WA
Ok, i think there is some confusion about the situation.

It is my understanding that what Jeff has is:

120' of 6/3 with ground that runs out to a fused disconnect box. From this box he has wired up the A/C unit. If this is true, there is an unused neutral wire in the circuit that could be used to make the 110v circuit.

"The A/C circuit terminates in a fused disconnect box, and then a whip into the unit."

If this is what he has, it is my understanding he could put an appropriate subpanel in place of this fused disconnect box (Might need to put in grounding rods and bar, i'm not sure) and then put in a appropriate 220 v breaker and 110 breaker.


However, maybe I have this backwards and the fuse disconnect box is the source.
 

JeffeVerde

Member
Messages
86
Reaction score
2
Points
8
Location
L.A.
Ok, i think there is some confusion about the situation.

It is my understanding that what Jeff has is:

120' of 6/3 with ground that runs out to a fused disconnect box. From this box he has wired up the A/C unit. If this is true, there is an unused neutral wire in the circuit that could be used to make the 110v circuit. . . .

Correct

Remove your outdoor A/C disconnect and replace it with a small weatheproof subpanel. Add the proper sized 2 pole breaker for the A/C and then add a 20A single pole breaker for your outside outlet. The subpanel will act as a disconnect for the A/C so you will no longer need the disconnect.

-rick

Thanks for your input, that's what I was thinking.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Ac

Right now, using common wiring pracices, the "third wire" should be the ground, NOT a neutral. IF so, and he converts it to a neutral, he WILL need a ground of some kind.
 

JeffeVerde

Member
Messages
86
Reaction score
2
Points
8
Location
L.A.
Right now, using common wiring pracices, the "third wire" should be the ground, NOT a neutral. IF so, and he converts it to a neutral, he WILL need a ground of some kind.

You're correct in that the whip to the device is just hot/hot/ground. But the existing wiring to the disconnect is a 3 conductor + ground NM-B --- maybe planning ahead for someone needing to split 110v off?
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Wiring

More likely an electrician who had the wire on his truck, or assumed that ALL 220/240 circuits needed a neutral, the same as electric ranges and dryers. Few would ever think ahead for that purpose, since a subpanel at an A/C unit would be a decidedly rare installation. Not all 6/3 wires have grounds, so until you specified that yours did it was not obvious. WHERE is that third wire connected now, since it should have no purpose in life, or need to exist.
 

JeffeVerde

Member
Messages
86
Reaction score
2
Points
8
Location
L.A.
More likely an electrician who had the wire on his truck, or assumed that ALL 220/240 circuits needed a neutral, the same as electric ranges and dryers. Few would ever think ahead for that purpose, since a subpanel at an A/C unit would be a decidedly rare installation. Not all 6/3 wires have grounds, so until you specified that yours did it was not obvious. WHERE is that third wire connected now, since it should have no purpose in life, or need to exist.


Sorry, I forgot to add :p after "planning ahead" :)

The NM-B terminates in a junction box, then jumpers for the hot pair run through a mud ring and bushing into the back of the disconnect box mounted outside. The neutral was capped off with a wire nut in the junction box.
 
Last edited:

CodeOne

Code Enforcement
Messages
160
Reaction score
0
Points
0
Location
North Carolina
I've got a 230v/50A circuit supplying the A/C compressor and the compressor only requries 35A, so overloading the 50A circuit isn't an issue. The A/C circuit terminates in a fused disconnect box, and then a whip into the unit.

What is the minimum circuit ampacity for you a/c?
What is the max breaker size for your a/c?

These facts are needed to do the calculation you need.
 

CodeOne

Code Enforcement
Messages
160
Reaction score
0
Points
0
Location
North Carolina
I've got a 230v/50A circuit supplying the A/C compressor and the compressor only requries 35A, so overloading the 50A circuit isn't an issue. The A/C circuit terminates in a fused disconnect box, and then a whip into the unit.

The issue is if your minimum circuit ampacity is 35A you haved to multiply 35 x 125% to come up with your calculated load for the circuit. This is for start up current.

35 x 125% = 43.75 or 44A
50A - 44A = 6A
Dont have as much extra as you thought!

Now if the 35A is you max breaker size you might be ok.
Give us some more info please.
 