is this legal?

Users who are viewing this thread

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
quick question

can you hook into the line from the toilet before it reaches the main stack?

here's a quick diagram showing the way it was hooked up. ideally I would hook up like this again.

legal.jpg


the branch from the sink/washer is a y connector on TOP of the 3 inch line, not on the side.

Pabs
 

Dcelite

Plumber
Messages
131
Reaction score
0
Points
0
Location
Los Gatos, CA
Website
www.merchantcircle.com
That 3" pipe going to the toilet flange is called the trap arm. You can not drain another fixture into a trap arm. You can only have one trap per trap arm. You would have to drain the sink into the stack.

DC
 

Dcelite

Plumber
Messages
131
Reaction score
0
Points
0
Location
Los Gatos, CA
Website
www.merchantcircle.com
If that toilet flange is 15' away from the stack then maybe that 2" is supposed to be the vent for the toilet. You would need to run a seperate line from the sink/washer and tie into the stack. The sink and washer, of course, need to be vented through the roof or tied into another vent.

DC
 

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
If that toilet flange is 15' away from the stack then maybe that 2" is supposed to be the vent for the toilet. You would need to run a seperate line from the sink/washer and tie into the stack. The sink and washer, of course, need to be vented through the roof or tied into another vent.

DC


makes sense about running separate lines to the stack. a little more work but not that much really.

the 2 (actually only 1 1/2) line was never intended as a vent. that reno was done by the previous owner. he's botched pretty much everything he's ever touched in that house..incredible.

as for that long run to the stack... you feel that's too long without a vent? that means that right now it gets its venting from the main stack that is a good 15 feet away (if not more)

If I use that 1 1/2 line as a vent, how far from the flange should I hook it up? and does anything else change downstream if I add that vent?

P
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
drain

That drain is acting as the toilet's vent, but as such it should be 2", but could be 1 1/2" depending on your code's requirements. If you repipe the sink drain to a new connection to the main stack, you will still have to provide the proper vent for the toilet.
 

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
thanks for all the help this far guys...this site is great!

ok...so how's this for my final plan... I hope ;)
vents.jpg


for the new vent for the toilet... can I tie that in to my 2 inch vent I'm using for the sink and washer?

otherwise I can go separate out the house... but rather only poke one hole in the house

also.. at the main stack...when I bring my new drain for the sink and washer (the 2 inch line), can I at that point tie it in to the pipe coming from the toilet? we are talking at least 15 feet at this point.. is there still a risk of siphoning ?? reason I ask is because it may be hard to connect to the main stack.. old cast...there's a small PVC section where the toilet line comes in but I rather not touch the main stack if I don't have too

also...the vent for the toilet... I have running up under the bathroom and out the wall...but cold I bring that vent back to the main stack? or is too long a run? just curious

thanks
 

Rmelz

New Member
Messages
1
Reaction score
0
Points
0
Location
Ohio
Is that sink a bathroom sink? If it is then you can wet vent the water closet with the sink. But no the drawing you made is not legal. The vent you have for the water closet is called a flat vent. Any vent that is horizontal has to be 6" minimum above the flood level rim of the highest fixture on that branch. If the vent is not 6" above the flr, the vent runs a chance of filling up with waste if the sewer ever backs up.
 

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
hey dcelite

I could bring the vent up the inside wall then out the top and make a bulk head to contain the vent until get back to the wall on the other side i guess

so that would mean I could tie in my 2" drain for the washer/sink anywhere at that point (after ny vertical vent) if I understand you correctly?

I'll draw up another plan...hopefully this one will be the last!
oh..and if I run the pipe behind, is there any restrictions regarding distance before it gets outside? I assume the only restriction is that the piep always be with an upward slope correct?
 

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
Is that sink a bathroom sink? If it is then you can wet vent the water closet with the sink. But no the drawing you made is not legal. The vent you have for the water closet is called a flat vent. Any vent that is horizontal has to be 6" minimum above the flood level rim of the highest fixture on that branch. If the vent is not 6" above the flr, the vent runs a chance of filling up with waste if the sewer ever backs up.

yes it is a sink . what do you mean when you say that I could wet vent the water closet with the sink?
 

Dcelite

Plumber
Messages
131
Reaction score
0
Points
0
Location
Los Gatos, CA
Website
www.merchantcircle.com
By George, I think you've got it! You needn't be concerned with the distance of the vent in this layout.
Don't worry about the wet venting for the sink. It won't be applicable if you run the toilet vent in a different wall.
 

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
ok, thanks to all your tip... I think this is my final layout! ...you be the judges!

check this out
finalb.jpg


the blue lines represent the parts that are vented.
yellow is where the water shall flow...
all pipes are 2" withe the exception of the vent for the washer and the p trap and trap arm of the sink.. they both tie into the 2" line that connects to the WC drain (after the new vent!)

the vent for the WC will run behind the wall and then come on in the corner. that's where I'll have to run a bulk head to get the other side of the bathroom.. .

both trap arms (sink and the washer) should run at 1/4 per foot correct?

also...does the vent need that slope (upward) as well, as minimuml? or as long as it's not going down it's fine?
 

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
That looks good. Vents need to be sloped but no minimum, the idea is to let condensation or rain that comes in at the roofcap drain back into the sanitary system.
 

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
gotcha...so even if I only dropped 1/4 of an inch of 6 feet or so that would be ok?

I'm trying to minimize the size of the bulk head...small bathroom so adding a huge bulk head will look funny.
the vent for the WC needs to be 2" correct?
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
I use 2" on the toilet vent.
This drawing looks much better.
Much better.

In Washington State, we would use a combo on it's back for the toilet vent. That would look like a wye and 45 together.
I don't know what the inspectors like in Canada.
They may be okay with the 3x2 Santee.
They used to be okay with them here too.

abs_wye_combo.jpg
 
Last edited:

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
I use 2" on the toilet vent.
This drawing looks much better.
Much better.


It's because of the all the colors eh? I put the EH in there just to confirm I live in Canada :)


I
In Washington State, we would use a combo on it's back for the toilet vent. That would look like a wye and 45 together.
I don't know what the inspectors like in Canada.
They may be okay with the 3x2 Santee.
They used to be okay with them here too.

oh... I think I know what you mean. actually I just drew it like that, I will use a wye and a 45 to go up through the ceiling...
next time I'll proof my drawings a little better....that's what happens when you do this stuff while at work... hehe

thanks for all the guidance guys... I will surely have a question or two before I'm completely done... but you've helped a great deal to get to this point...

off to do some electrical now
too late to be drilling holes right now... don't think the family would appreciate it much :)
 

Pabs

New Member
Messages
22
Reaction score
0
Points
0
Location
Moncton, NB (Canada)
hey Terry

finally got to the dry fit of all my pipes...

got his hooked up for the WC drain and vent
IMG_0001.jpg


it was a bit of a challenge getting the vent in but I think I got it

one regarding the vent...am I OK with the the of connector showing in my pic?
The Y is going in the opposite direction as the flow.... is this how you should hook it up?