just curious. Is it possible to add more pressure after the spigot outside? I mean, is there a product that can be added in between the outside spigot and the sprinkler head so that it can handle more sprinkler head or maybe more water per gallon?
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
I'm afraid not. You are limited by the water supply line size and pressure from the source. I don't have a clue what you mean by. "more water per gallon".:confused:
 

V1rtu0s1ty

DIY Senior Member
Messages
151
Reaction score
0
Points
0
Location
Chicago IL
I remember my dad when I was young, he had a motor about 12 inch long and 6-7inch in diameter. It sucks water from the ground and services all our spigots/faucets/shower in the whole house.

I was thinking that if I put a motor in between to suck more water from the spigot, it will work. However, the water back then was in idle state.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
pressure

The "spigot" has a TREMENDOUS pressure drop because it only has a 3/8" hole for the water to flow through it. Changing to a proper connection will increase the volume tremendously. But the proper connection is more than just a tee and a valve with the irrigation line connected to it.
 

V1rtu0s1ty

DIY Senior Member
Messages
151
Reaction score
0
Points
0
Location
Chicago IL
The "spigot" has a TREMENDOUS pressure drop because it only has a 3/8" hole for the water to flow through it. Changing to a proper connection will increase the volume tremendously. But the proper connection is more than just a tee and a valve with the irrigation line connected to it.

Ah, you are right. That 3/8" hole will prevent a lot of good gallons. I remember seeing a different spigot. Or maybe I'm referring to a shut off valve. I remember seeing a 1" brass shutoff valve at M3nards.

By the way, I ran out of time and wasn't able to install underground sprinkler. Instead, I just use garden hose and it's working pretty well. I have a question though. What if I put another pipe with a shutoff valve inside the basement and let it out that same wall? Then hook the diy spinkler valves directly to the new pipe? I'm sure when it's checked by village, it will not be approved but it doesn't really differ from the other pipe design that has spigot. I won't have it checked as well. :D

There is a possibility that I might change the pvc pipes since it won't fit anymore on the new 3/4" or 1" pipe.

lawnsprinklervalves20090814.jpg
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
valve

1. The spigot is a legal connection because it has a vacuum breaker on it, but ONLY if you open and close the valve during the operation of the sprinkler system, because it is an ATMOSPHERIC vb, and not a pressure one which is required WHENEVER the water is always turned on to the valve inlets.

2. If you make a connection in the basement, then you NEED a pressure vacuum breaker/backflow preventer where you make the connection. It WILL discharge water periodically, especially when the water is turned on or off to it, or the house, so it should be in a "safe" location.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
If your booster pump doesn't cavitate it should work.

I'm still waiting to hear from my water company what kind of PSI and GPM I can expect at my house entrance [the pump curve]. The PSI is probably between 30 and 80.

Once I know this and calc. the pipe loss I should be able to spec'y a pump just like you're talking about.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
If those inline valves are below grade, then I don't think that the vacuum breaker hose bibb meets code for backflow prevention.
 

tomm

New Member
Messages
41
Reaction score
0
Points
0
If those inline valves are below grade, then I don't think that the vacuum breaker hose bibb meets code for backflow prevention.

Huh? whats below grade gotta do with it?

That whole setup doesn't meet code.

Valves after the avb and that additional hose bibb after avb being the biggest problems.

I can see that whole setup blowing up and flooding into the window well, but that's just me!
 