If you were to guess, How old would you say these fuse's are?

Not even sure what the one on the right is .... Should these be in a 5 ton heat pump rated for 50amp? They are 45amp.
 

Attachments

  • Fuse 007.jpg
    Fuse 007.jpg
    41.1 KB · Views: 242

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Well, I don't think you see Gould fuses any more. I could be wrong, but I think FerrazShawmut bought up that brand.

Anyway, 45 amps could be in the ballpark for a 5 ton condenser.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
Should these be in a 5 ton heat pump rated for 50amp? They are 45amp.
I got 24A for a 5 ton heat pump with COP = 3 at 240v. Start up current may be 6x higher.

Wrap the fuse in several layers of newspaper and hit it with a hammer. If the fuse element inside is only cracked in one place it was a fatigue failure or a mild overload. If the element is splattered it was a heavy overload.
 