I think the answer is yes but i just want to make sure.

I already have a 10 gague home run that goes to my garage. Currently it is disconnected at the panel and in the garage it just runs to a box where the wires are capped. Can I just connect this to a 20 amp breaker in the panel and put a regular receptical at the garage end? GFCI of course : )


Thanks
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
10/2 with ground I presume?

Safety wise, it is fine to use a larger than required wire.

Mechanical wise, a #10 should fit in the breaker OK (look at specs on breaker), but might not in the GFCI. The new GFCI's I've seen have a hole in the back for the wire and you tighten the connection with the screw on the side - can't wrap the wire around the side and I don't think you would want to try that with a #10 anyway. But the hole on one I have here looks like #12 is the largest it will accept, but mine is a 15 amp. Maybe a 20 amp GFCI would accept a #10? I don't know?

I don't see wire sizes when looking at the GFCI specs on the internet.

Then cramming everything into the electrical box wise... I would use a deep double gang box with a single gang plaster ring.
 

Iminaquagmire

DIY Senior Member
Messages
206
Reaction score
0
Points
0
NO PIGTAILING. What happens when somebody comes in and sees that 10-2 and decides to up the breaker? A responsible person would check first, but a lot would see the 10-2 and add a new breaker, overloading any pigtailed 12ga.

Cooper GFCI's can handle 10ga solid or stranded in the backwire holes and I believe 8ga in the screw terminals.
 
Last edited:

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
NO PIGTAILING. What happens when somebody comes in and sees that 10-2 and decides to up the breaker? A responsible person would check first, but a lot would see the 10-2 and add a new breaker, overloading any pigtailed 12ga.

Cooper GFCI's can handle 10ga solid or stranded in the backwire holes and I believe 8ga in the screw terminals.

Duh, the same thing that happens when somebody ups the breaker without checking in the 1st place with 20a devices in place
#10 wire is commonly used for long 20a runs
When have you last seen a 30a residential outlet 120v :confused: :rolleyes:
 

99k

Radon Contractor and Water Treatment
Messages
460
Reaction score
2
Points
0
Location
Fairfield Co.,Connecticut
Website
www.78radon.com
Duh, the same thing that happens when somebody ups the breaker without checking in the 1st place with 20a devices in place
#10 wire is commonly used for long 20a runs
When have you last seen a 30a residential outlet 120v :confused: :rolleyes:


I'm no electrician but I have to agree ... pigtail is fine. My electrician does this.
 

Iminaquagmire

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Duh, the same thing that happens when somebody ups the breaker without checking in the 1st place with 20a devices in place
#10 wire is commonly used for long 20a runs
When have you last seen a 30a residential outlet 120v :confused: :rolleyes:

I've never seen a 30A residential receptacle. That doesn't mean somebody down the line can't change the line to something else or add a junction elsewhere. Like I said, a responsible person would check before changing a breaker, but I'll never pretend everybody is responsible or smart.

You can put aside the average person's intelligence anyway, as there is no need to pigtail in this instance. 10ga wire will connect just fine to either Leviton or Cooper GFCI receptacles.
 

Scuba_Dave

Extreme DIY Homeowner
Messages
868
Reaction score
2
Points
0
Location
South of Boston, MA
Website
holidaves.com
I've never seen a 30A residential receptacle. That doesn't mean somebody down the line can't change the line to something else or add a junction elsewhere. Like I said, a responsible person would check before changing a breaker, but I'll never pretend everybody is responsible or smart.

You can put aside the average person's intelligence anyway, as there is no need to pigtail in this instance. 10ga wire will connect just fine to either Leviton or Cooper GFCI receptacles.

And you can't possibly plan for everything somebody else might do
Telling someone they can't do it is wrong
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
back wiring

A few years back restrictions were placed on back wired devices. The holes could not accept a larger wire than the device was rated for. #14 ONLY for 15 amp items, #14 or smaller for 20 amp ones. Therefore the #10 wire will not fit into a back wired receptacle, but would work with screw terminals or devices with wired connectors.
 

gogden56

New Member
Messages
1
Reaction score
0
Points
0
The number 10 wire is good for 30 amps. That is max. Yes you can use it for a smaller breaker.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
NO PIGTAILING. What happens when somebody comes in and sees that 10-2 and decides to up the breaker? A responsible person would check first, but a lot would see the 10-2 and add a new breaker, overloading any pigtailed 12ga.

Cooper GFCI's can handle 10ga solid or stranded in the backwire holes and I believe 8ga in the screw terminals.


Your a goof ball. :D Who cares what the next idiot does?
 

rgsgww

New Member
Messages
52
Reaction score
0
Points
0
Location
Ia
The next idiot may tap off the service conductors, how am I suppose to prevent that? :D
 

GabeS

Remodel Contractor
Messages
293
Reaction score
0
Points
0
Location
Brooklyn NY
20 amp breaker means 20 amp circuit. The breaker determines the amps of the circuit, not the wire size. If someone switches to a higher breaker, then they don't know what they are doing and shouldn't be doing it. How can you prevent them from sticking a live wire in their mouth?
 

Iminaquagmire

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Okay, maybe you shouldn't care what the next idiot does. After all it doesn't affect you in the least. When I have to go pull the idiot's body out after his house catches fire, it makes me care.

Make your smaller pigtails and branches all you want, just don't do it in my town.

Anyways, the next idiot that comes along aside, there is no need to pigtail here. Look up the Cooper GFCI pdf. It can be installed with 10ga just fine.
 
Last edited:

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
Okay, maybe you shouldn't care what the next idiot does. After all it doesn't affect you in the least. When I have to go pull the idiot's body out after his house catches fire, it makes me care.

.
The next idiot shouldn't be touching the panel box unless he knows what he is doing in the first place (e.g.: licenced electrician), and the electricians that I know will always double check a circuit 20 amps or higher to see where it leads, escpecially when there is no ryhm or reason for a 20 amp breaker to be there.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks