Question:

I've seen breakers sold at the Big Boxes that have clips connecting two breakers to force a common trip but are there any aftermarket connectors or clips available that can make two standard 1-pole breakers into a common trip set? Would this be acceptable under the NEC?

Gracias!
 

MaintenanceGuy

In the Trades
Messages
106
Reaction score
1
Points
0
Location
Pennsylvania
Breaker ties do not make breakers common trip. They force the person turning off a breaker to turn off both (or all three) poles. With breaker ties installed between breakers, when out breaker trips, it will not open the other breaker.

Only two pole (or on 3Φ service, 3 pole breakers) purchased as one assembly will open all phases when one phase trips.
 

GabeS

Remodel Contractor
Messages
293
Reaction score
0
Points
0
Location
Brooklyn NY
Just a thought. Why not just remove the singles and put in a double. Do it right. Sleep at night.
 

MaintenanceGuy

In the Trades
Messages
106
Reaction score
1
Points
0
Location
Pennsylvania
The DO pull the second breaker open during a trip, otherwise the unsafe condition would still exist, and some manufacturers do make them.

I disagree. Two pole breakers are common trip. Two single pole breakers with a handle tie are not common trip. Breakers are designed to trip even if the handles are restrained for some reason. They even make a clip to lock a breaker handle in the "on" position for critical equipment that can't be turned off. These breakers still trip properly even though the handles can't move.

Here's one manufacturer's thoughts on the matter. Sorry for the poor quality. Tried to upload a PDF, file was too large for this site. So I converted to gif, uploaded, and this site converted again to JPG. so it's been tampered with and compressed 3 times. Hope it's readable.
 

Attachments

  • handle_ties.jpg
    handle_ties.jpg
    65.8 KB · Views: 1,628

Jar546

In the Trades
Messages
424
Reaction score
0
Points
0
Location
USA
Website
www.inspectpa.com
A handle tie rated for the application and breakers can be used for a two pole application and be NEC compliant.
 

MaintenanceGuy

In the Trades
Messages
106
Reaction score
1
Points
0
Location
Pennsylvania
A handle tie rated for the application and breakers can be used for a two pole application and be NEC compliant.

Not always. Not for multiwire branch circuits serving other than line-to-neutral loads. I'm looking at the 2005 NEC. 210.4 (C) Exception No. 2. I don't know if this changed in the 2008 or what code the OP is under.

"Where all ungrounded conductors of a multiwire branch circuit are opened simultaneously by the branch circuit overcurrent device."

I don't believe that a handle tie meets the requirement of all circuits being opened simultaneously BY THE OVERCURRENT DEVICE.
 

BrianJohn

DIY Senior Member
Messages
150
Reaction score
0
Points
0
Location
Virginia
Breaker ties do not make breakers common trip. They force the person turning off a breaker to turn off both (or all three) poles. With breaker ties installed between breakers, when out breaker trips, it will not open the other breaker.

Only two pole (or on 3Φ service, 3 pole breakers) purchased as one assembly will open all phases when one phase trips.



Wrong.

A handle tie when installed either a legal tie or a 1/8 toggle bolt through the handle (NOT APPROVED, though illegal handle ties are illegal because they are not tested to operate under any condition) will result in opening of both CBs with a trip (fault) on one of the conductors.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Wrong.

A handle tie when installed either a legal tie or a 1/8 toggle bolt through the handle (NOT APPROVED, though illegal handle ties are illegal because they are not tested to operate under any condition) will result in opening of both CBs with a trip (fault) on one of the conductors.


This is a false statement. Handle ties does not open both breakers in a fault in one breaker.

Listen one more time handle ties does not open both breakers in a fault condition of only one ungrounded conductor.

Handle ties does not operate both breakers in a fault condition

Handle ties does not trun off both breakers in a fault condition..

Only two pole breakers will open both circuits in a fault condition
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
Personally, I spent an hour troubleshooting because a two-pole breaker with connecting pin only tripped on one side and I didn't notice that only one pole was tripped.
 