Oven Range hookup

Users who are viewing this thread

Jerome8283

New Member
Messages
140
Reaction score
0
Points
0
Location
New York
The new range I would like to purchase requires a 40amp circut but I have a 50amp. Can I hookup this range to the 50amp?

Also the wiring is coming from the wall, not connected to an oulet. What would be the cost to install a 3 prong oulet?
 

Jar546

In the Trades
Messages
424
Reaction score
0
Points
0
Location
USA
Website
www.inspectpa.com
Sure why not, do it and don't worry about the data plate on the range. I don't know why they put them on there anyway.

Outlet is under $10. so DIY.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
The new range I would like to purchase requires a 40amp circut but I have a 50amp. Can I hookup this range to the 50amp?
Why not just install a 40 amp breaker? It is fairly easy to do!

Also the wiring is coming from the wall, not connected to an oulet. What would be the cost to install a 3 prong oulet?
4 wire, four conductor, 4 conductor, four wire.

I hope I made it clear enough that you will need two hots, a neutral and an equipment grounding conductor for that brand new range that you are going to change the 50 amp breaker to a 40 amp breaker and install 4 conductor cable to supply?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Those guys sometimes get kind of flippant (usually justified, but not always!). On a dedicated circuit, your CB should match the manufacturer's specification. Current codes also require this to have the 4-wire cable. So, if the wire is 4-wire, (and it was sized properly when installed), you can pop out the old CB, put in a 40A one, and put in a new appropriate plug. There's no problem having larger wire than required for the load (as long as it will fit into the connectors), but you can't have smaller wire than specified for the CB you use.

If the wire size or conductor count isn't sufficient, the whole thing needs to be rewired.
 

Jerome8283

New Member
Messages
140
Reaction score
0
Points
0
Location
New York
I just had a new range delivered and installed by the appliance retailer. My house is 15 years old and I am aware of the recent code change from 3 to 4 wire. According to the installer, the ranges don't come with cords. They have an assortment in the truck, find out what kind of outlet you have, and match the cord to it.

I don't have an outlet. The wire comes directly from the wall hard wired to the current range. The label on the range states (3 wire).

The manufacture manual states the following;

Installation Instructions
ELECTRICAL CONNECTIONS
You must use a 3-wire, single-phase A.C.
208Y/120 Volt or 240/120 Volt, 60 hertz
electrical system.
If the electrical service provided does not
meet the above specifications, have a
licensed electrician install an approved outlet.
Use only a 3-conductor or a 4-conductor
UL-listed range cord. These cords may be
provided with ring terminals on wire and
a strain relief device.
A range cord rated at 40 amps with 125/250
minimum volt range is required. A 50 amp
range cord is not recommended but if used,
it should be marked for use with nominal
13⁄8″ diameter connection openings. Care
should be taken to center the cable and
strain relief within the knockout hole to keep
the edge from damaging the cable.
• Because range terminals are not accessible
after range is in position, flexible service
conduit or cord must be used.
NOTE: If conduit is being used, go to Step 3D
and then to Step 6 or 7.
• On some models, a filter capacitor may be
connected between the black and white
leads on the junction block.
ALL NEW CONSTRUCTIONS,
MOBILE HOMES AND
INSTALLATIONS WHERE
LOCAL CODES DO NOT
ALLOW GROUNDING
THROUGH NEUTRAL,
REQUIRE A 4-CONDUCTOR
UL-LISTED RANGE CORD.
ELECTRICAL REQUIREMENTS
CAUTION: For personal safety,
do not use an extension cord with this
appliance. Remove house fuse or open circuit
breaker before beginning installation.
This appliance must be supplied with the
proper voltage and frequency, and connected
to an individual properly grounded branch
circuit, protected by a circuit breaker or fuse
having amperage as specified on the rating
plate. The rating plate is located on the left
hand side of the lower oven front frame.
We recommend you have the electrical wiring
and hookup of your range connected by a
qualified electrician. After installation, have
the electrician show you where your main
range disconnect is located.
Check with your local utilities for electrical
codes which apply in your area. Failure to
wire your oven according to governing codes
could result in a hazardous condition. If there
are no local codes, your range must be wired
and fused to meet the requirements of the
National Electrical Code, ANSI/NFPA No. 70–
Latest Edition. You can get a copy by writing:
National Fire Protection Association
Batterymarch Park
Quincy, MA 02269
Effective January 1, 1996, the National
Electrical Code requires that new construction
(not existing) utilize a 4-conductor connection
to an electric range.
Location of
model rating
plate
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
power

The label on the range states 3 wire, but that is only for the power source. New units still have a 3 wire power source but also a fourth wire for the grounding requirement. Older systems combined the neutral and ground so they only had 3 wires to the appliance. The outlet and range cord used will depend on which type of circuit you have.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
I hate that they put that "3-wire" crap on there. It only confuses things because they do not say "3-wire plus ground", or something else for existing installations.
Those words are not at all necessary. "120/240" is all that is needed.
 

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
I hope you removed the jumper on the range as per the instructions for a four wire install.

Often overlooked by my fellow DIYers but essential.

And equally important, the wire must be of the correct gauge.

Using 4-wire for a range is a heavy, hard job. I did not enjoy running fifty feet of that.

I'd hire a pro next time just to save my back.
 
Last edited:

electrotuko

Member
Messages
58
Reaction score
0
Points
6
Location
Austin, TX
I would appreciate for devise installing a wall oven, requires installation of 50A power line.
I will be using a ½ inch flex metal conduit from the electrical box to the oven location. Four 8 AWG THHN stranded wires will be running through (I have checked, they fit easily) the conduit.

My question, should I use 8 gauge wires for only L1 and L2, and for N and GND use a smaller 10 AWG wire, since they will not conduct the same high current as L1, L2?

The reason for question: In the electrical stores I have seen a power cord for the 50A rated oven (flex rubber cable as a replacement from the oven to the outlet) made in this way - two wires 6 gauge, two 8 gauge.
 

Jar546

In the Trades
Messages
424
Reaction score
0
Points
0
Location
USA
Website
www.inspectpa.com
I would appreciate for devise installing a wall oven, requires installation of 50A power line.
I will be using a ½ inch flex metal conduit from the electrical box to the oven location. Four 8 AWG THHN stranded wires will be running through (I have checked, they fit easily) the conduit.

My question, should I use 8 gauge wires for only L1 and L2, and for N and GND use a smaller 10 AWG wire, since they will not conduct the same high current as L1, L2?

The reason for question: In the electrical stores I have seen a power cord for the 50A rated oven (flex rubber cable as a replacement from the oven to the outlet) made in this way - two wires 6 gauge, two 8 gauge.

1) 8AWG (I assume you mean copper) is not rated for 50A.
2) You cannot legally place 4 #8 THHN in 1/2" FMC

You will need to follow the data plate rating and the manufacturer's installation instructions for the installation.

Is this a residential or commercial setting?

If the cable is using #6 then why would you think you could downsize the branch feeder?

Since you appear to not know what to do and you are dealing with a 240vac system, I would recommend a professional, licensed, qualified electrician do the work for you.

I am sure you could get it to work like many people do but that does not mean that it was done correctly or SAFE.

Electrical work is not a hobby.
 

electrotuko

Member
Messages
58
Reaction score
0
Points
6
Location
Austin, TX
jar546, thanks for your comments.
Yes, this is a residential setting.
Yes the wires are copper wires.
I have checked the specifications for the THHN copper stranded wires; they are rated 50A at 75 deg. C.
The same information was given to me in a local Home Depot store where I bought the wires.

What is the current rating for the 75 deg. C rated 8 AWG THHN stranded copper wires included in a FMC for the residential applications?

My assumptions, correct me if I am wrong:
The replacement 50A cable uses 6 AWG wires most likely because it is a thick rubber cable, the wires inside do not have enough ventilation, plus the cable is flexible, not the stationary.

I am curious if the all conductors in the cable intended to be used in the oven application where the neutral is carrying low current, need to be the same gauge?
Again, the replacement 50A cable you may buy in the store has 2-wires #6 and 2-wires #8.
 