code compliance - GFCI and tamper resistant

Users who are viewing this thread

Beekerc

IT Consultant / Network Engineer
Messages
94
Reaction score
0
Points
0
Location
Seattle
2 questions, but both relating to NEC code

1) code says that receptacles (excluding appliances) in a garage must be GFCI. if I am wiring outlets along a work bench (approx 36 to 48 inches off the floor if that matters). do i need put a GFCI receptacle in each outlet box? or can i put one GFCI at the first outlet box then connect the down-line non-GFCI (read: much cheaper) receptacles to the GFCI's LOAD side?

2) I read that tamper resistant receptacles are required for all new residential constructions starting in 2008. does that cover new circuits installed into existing homes (ie. circuit expansions, remodelling)? I wouldn't think so and that it just refers to houses that are being built from the ground up, but I haven't studied the NEC code so I don't know *all* of rules or interpretive nuances.

Thanks
BeekerC
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
on #1, you can use a GFCI breaker, or one outlet, with the rest fed-through it.
 

Johnny C

Electrician
Messages
23
Reaction score
0
Points
0
Location
Mass. & now Virginia Beach, VA
Tamper resistant recept.

All 15 and 20 ampere receptacles installed in accordance with Section 210-52 are required to be of the "tamper resistant" type. That covers just about all 15 and 20 amp receptacles at a house. (OUCH)
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
All 15 and 20 ampere receptacles installed in accordance with Section 210-52 are required to be of the "tamper resistant" type. That covers just about all 15 and 20 amp receptacles at a house. (OUCH)
Keep in mind this is a change for the new 2008 NEC, and only applies if your area is under that code (or similar amendments). Not nearly all areas follow the 2008 NEC.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
1) code says that receptacles (excluding appliances) in a garage must be GFCI. if I am wiring outlets along a work bench (approx 36 to 48 inches off the floor if that matters). do i need put a GFCI receptacle in each outlet box? or can i put one GFCI at the first outlet box then connect the down-line non-GFCI (read: much cheaper) receptacles to the GFCI's LOAD side?
Well, appliances with strict limitations under the 2005 NEC.


(A) Dwelling Units All 125-volt, single-phase, 15- and 20- ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.

(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas, and
areas of similar use

Exception No. 1 to (2): Receptacles that are not readily
accessible.

Exception No. 2 to (2): A single receptacle or a duplex
receptacle for two appliances located within dedicated space
for each appliance that, in normal use, is not easily moved
from one place to another and that is cord-and-plug connected
in accordance with 400.7(A)(6), (A)(7), or (A)(8).



Under the 2008 NEC ALL 125v 15 & 20 amp receptacles must be GFI protected.
 
Last edited:

Johnny C

Electrician
Messages
23
Reaction score
0
Points
0
Location
Mass. & now Virginia Beach, VA
GFCI's

To BEEKERC, You can install one GFCI receptacle feed other downstream receptacles from the load-side of the GFCI receptacle and they will be GFCI protected. You must place a label on the regular receptacles to indicate that they are GFCI protected.
 

Beekerc

IT Consultant / Network Engineer
Messages
94
Reaction score
0
Points
0
Location
Seattle
thanks for the good info

To BEEKERC, You can install one GFCI receptacle feed other downstream receptacles from the load-side of the GFCI receptacle and they will be GFCI protected.

since i'm planning on putting the left and right halves of the garage on their own circuit, the demarcation point being the garage door into the basement, i was going to put a 2-gang box by the door and put a pair of dead-face GFCI's, that way i always know where to go when it trips. i know it's not as cost effective as making the first outlet in the run a GFCI receptacle, but it's the convenince of location, and i plan to pick a device that has both a green (on-line) and red (tripped) indicator light so you can see them from across the room.

You must place a label on the regular receptacles to indicate that they are GFCI protected.

ah, that's what those labels that come with the GFCI outlets are for. :)

RE: tamper resistant outlets, i still haven't gotten a definitive answer as to whether or not our locale has adopted 2008 code yet, or if the tamper resistant only applies to new constructions vs new circuits in a remodel. however, 30~50 plastic outlet plugs can be had for the same price as a single tamper resistant receptacle, and while my kids haven't yet been able to pull out a safety plug, i don't put it past them to try and stick two flat objects into an outlet at the same time, which defeats the tamper resistant device. for that matter, even if tamper resistant receptacles were required, i'd still probably put the plastic plugs in them anyway.

thanks to all for the info and advice.
 