Medicine Cabinet with 15 amp receptacle

Users who are viewing this thread

dcd

New Member
Messages
3
Reaction score
0
Points
0
I bought a Broan 455FL medicine cabinet for a bathroom. It has a single 15 amp receptacle and 2 fluorescent lights. This would be the only receptacle in the bathroom. Its a grounded outlet but not a gfci so my thought is to put a gfci breaker in at the panel. I know bathrooms need to be on a 20 amp w/12-2. So if I have 1 15 amp receptacle and 12-2 going to the bathroom, what can be done to get the medicine cabinet wired safely?
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
medicine cabinet

As far as I know, medicine cabinet receptacles have been outlawed for decades, but since you have one and appear to want to use it, it must be on a GFCI circuit because by definition it will be over the sink.
 

dcd

New Member
Messages
3
Reaction score
0
Points
0
The cabinet is brand new, I'm not sure why Nutone would be selling it if it was outlawed.
Thanks for the tip.
Would I need to wire an additional receptacle upstream from the cabinet?
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Its not outlawed, but here is the problem, is it really a duplex receptacle or just a single receptacle?


Never mind, you made that clear, the only problem I see is that your still going to need the required 20 amp "WALL" receptacle within 3' of the sink to meet code.
 
Last edited:

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
outlets

You would be surprised how many "illegal" things are sold by stores like HD and Lowes. Medicine cabinet outlets used to be an automatic thing back in the 50's and 60's, but I have not even seen one in decades, so I assumed no one was producing them any more.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
As far as I know, medicine cabinet receptacles have been outlawed for decades, but since you have one and appear to want to use it, it must be on a GFCI circuit because by definition it will be over the sink.

Over the sink has nothing to do with the GFCI requirement. just FYI. :)
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
You would be surprised how many "illegal" things are sold by stores like HD and Lowes. Medicine cabinet outlets used to be an automatic thing back in the 50's and 60's, but I have not even seen one in decades, so I assumed no one was producing them any more.

Why would you say its outlawed though?
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
over the sink

Not a GFCI problem but having the cord coming down above the sink could induce the person to use it there and thus have a greater chance of accidently dropping into any water in the sink. They were never "duplex" outlets, but the older ones also did not have room for a grounding outlet. Now the cabinets with the lights and outlet on the side might be somewhat safer, but I would still go with the wall outlet.
 