Underground pipe install.

Users who are viewing this thread

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Hey all,

I’m going to install a ¾†main water line, (from the water meter to the house). In some areas here in Phoenix, the soil is aggressive, and will deteriorate copper pipe from the outside inward. Is it a good idea to bed and shade the copper pipe with sand, or just wrap it with pipe plastic sheathing? Or, would it just be better using schedule 40 or 80 plastic, (glue together) pipe?

Thanks, Mike
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
If agressive soil prevent a long life for copper then why not pursuit other options for materials. See what is allowed. PEX, PVC, & Black Polyethylene are all used in other areas of the country and hold up quite well.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
pipe

We usually only use PVC when the line has to be 1 1/4" or larger. I have installed many, many copper water lines all over Phoenix, and have never had any fail because of the soil conditions. I have repaired some which deteriorated because they were in a spot which was always wet, however.
 

NHmaster

Master Plumber
Messages
3,176
Reaction score
5
Points
0
Location
S. Maine
Most of the local water dept's out here have gone to sch 80 polyethelyne. cheap and effective.
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Thanks

If agressive soil prevent a long life for copper then why not pursuit other options for materials. See what is allowed. PEX, PVC, & Black Polyethylene are all used in other areas of the country and hold up quite well.

Thanks...I will look into what is allowed, (per code) here in Phoenix. The copper I have ran into that went bad was around 15 years old. The whole house had to be re-plumbed.

Thanks!

Mike
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Unless you have a one bath home, the 3/4" will be undersized.

Thanks Terry. I did check out your pipe sizing page. This house is kind of in the older side of town, and I will be looking at it tomorrow. A lot of the older homes were plumbed in with 3/4" and even to top it off, the used galvaized pipe. The owner told me over the phone that his was galvanized, and the volume is really bad. I find out tomorrow, what size his meter is, and what size he has going into the home.
On your chart, I noticed that even if you only have a 3/4" meter, you can pick up some fixture units by installing 1" of 1-1/4 pipe...interesting. Although, if it went beck to ¾†at the house, you probably wouldn’t pick up much, unless there was a hose bib there, or an irrigation system branch off there outside of the house.

Thanks again,

Mike
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
We usually only use PVC when the line has to be 1 1/4" or larger. I have installed many, many copper water lines all over Phoenix, and have never had any fail because of the soil conditions. I have repaired some which deteriorated because they were in a spot which was always wet, however.

Here are some photos of a house, where the copper pipe under the slab was leaking. The first repair was about 12 years after the house was built, and then I did another repair about 15 years after the house was built.
 

Attachments

  • Ed's trench 2.jpg
    Ed's trench 2.jpg
    46.1 KB · Views: 507
  • HPIM2039-1.jpg
    HPIM2039-1.jpg
    42.9 KB · Views: 518
  • HPIM2042.jpg
    HPIM2042.jpg
    42.9 KB · Views: 499
  • HPIM2044.jpg
    HPIM2044.jpg
    29.1 KB · Views: 478
  • HPIM2043.jpg
    HPIM2043.jpg
    28.5 KB · Views: 521

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
copper

Interesting. I have NEVER had a house in Phoenix that had that problem. And only a couple of under slab leaks that could not be attributed to poor workmanship during the original installation.
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Yep

Interesting. I have NEVER had a house in Phoenix that had that problem. And only a couple of under slab leaks that could not be attributed to poor workmanship during the original installation.


Yep, before I did the repair and pour back at his house, I begged the home owner to call a licensed company to do a complete re-plumbing on his house. He told me that if I don’t want to do the repair, that he would get someone else to do it. So I did the repair, and the pour back, and needless to say about 3 months later, he did get a complete re-plumb job.
His house is located on the North side of Camelback mountain, (if you know the area of Phoenix). And remember, this house was around 15 years old.

Thanks, Mike
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
if you only have a 3/4" meter, you can pick up some fixture units by installing 1" of 1-1/4 pipe...

Yes, it has to do with friction loss.
If you order a milk shake and use the small straws, it takes a long to suck it up. Same thing with a small straw, I mean pipe that is any kind of distance. It's slows down the water considerably.
A larger pipe, like a 1-0" or 1-1/4" reduces drag.

The only time that I have installed a 3/4" water service was to a one bath home. And most of the time, I installed a 1" pipe anyway. There is almost no cost difference, and it future proofs the home for any added plumbing or bathrooms later.

Two bath homes need 1" services
Three bath homes need at least a 1" and in some cases 1-1/4"
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Back to you....

Yes, it has to do with friction loss.
If you order a milk shake and use the small straws, it takes a long to suck it up. Same thing with a small straw, I mean pipe that is any kind of distance. It's slows down the water considerably.
A larger pipe, like a 1-0" or 1-1/4" reduces drag.

The only time that I have installed a 3/4" water service was to a one bath home. And most of the time, I installed a 1" pipe anyway. There is almost no cost difference, and it future proofs the home for any added plumbing or bathrooms later.

Two bath homes need 1" services
Three bath homes need at least a 1" and in some cases 1-1/4"


Thanks Terry…I did go check out the existing water service, and it was a ¾†galvanized line, with a 5/8†water meter. It’s kind of typical out here in the older part of town. One of the draw backs of putting in like PEX pipe, (or another nonmetallic type pipe) is that I will loose the grounding to the house. If I do install a nonmetallic pipe, (per code) I will have to install two ground rods, six feet apart, and then clamp them, via #4 copper wire, to the hose pipe…nothing ever easy! The run, (meter to house) is only about 40 feet, so maybe up-sizing would make a little difference, but with a 5/8†meter, I’m not sure if it would be noticeable.

Thanks big T,

Mike
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
but with a 5/8†meter, I’m not sure if it would be noticeable.

My mothers home has a 5/8" meter. I changed the water line from a 3/4" to 1.5" water lines. It made a huge difference.
She is 250 feet from the meter, but to give a simple example, on the irrigation on the back side of her property, I ran a 1-1/2" PVC line 250 feet, and then downsized to 1" for another 100 feet. The irrigation works that way on the back zone.
With the 3/4" line, it didn't work.
It's the same 5/8" meter.
She runs four zones on her one acre property.
 
Last edited:

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
Underground piping

Too bad you are not a plumber and don't know the correct way to repair a copper pipe under slab
 

psolutions

New Member
Messages
35
Reaction score
0
Points
0
Location
South Carolina
Plumbing Water Main

I would run pex. Its rather inexpensive and is very good against freezing. It would hold up against the water conditions.

About your grounding problem. I would seriously add two grounds anyway and get away from grounding to the water piping.

What you should be looking to do is set it up for the least expensive future maintenance with the least potential chance for future problems. I believe this would be pex piping with a proper ground.

Ask your electrician though...
 

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
With old homes that use the water service as a ground, it's always a good idea for an electrician to properly ground the panel before the plumbing replacement is done.
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Not a plumber

Too bad you are not a plumber and don't know the correct way to repair a copper pipe under slab


I have done proper under slab copper pipe repair by brazing the pipe together with oxygen and Mapp gas….â€even though I’m not a plumberâ€. Thank you for your concern.
 

Mikebarone

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Location
Phoenix, AZ
Thanks much!

I would run pex. Its rather inexpensive and is very good against freezing. It would hold up against the water conditions.

About your grounding problem. I would seriously add two grounds anyway and get away from grounding to the water piping.

What you should be looking to do is set it up for the least expensive future maintenance with the least potential chance for future problems. I believe this would be pex piping with a proper ground.

Ask your electrician though...


I have been doing some research on using PEX pipe. I have read on the pipe itself, and it recommended not be used if the free chlorine is over 4 PPM. I called the city water quality department and I guess the highest level they have ever put in the lines was 2 PPM, and that was just after 911. They said after time, they went back down to 1 PPM.
I will check with my electrician on getting it grounded…(and that will be me).

Thanks for the insight on the PEX,

Mike
 