AFCI Circuit trips when I turn on lights

Users who are viewing this thread

Keith Wolf Ent

New Member
Messages
8
Reaction score
0
Points
0
has about 4 plugs and 4 lights/switches on it - all 110v/60cycles, on a 20 amp AFCI breaker: 4 wall outlets (2 in master BR), (1) GFCI outlet, (2) motion detectors (Incandescent), with bathroom bulbs over the sink on one and an overhead light on the other, a bath fan and an outdoor spot fixture w/2 bulbs...
Is there too much going on/conflicts? Advice please... Thx!

P.S: I didn't install this circuit!:(
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Don't rule out the possibility that you're actually generating an arc when you turn on the lights, and the AFCI is doing its job. Could be a bad switch, bulb socket, wiring, etc.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
i would go with sloppy wiring, and a bad neutral to ground connection. Remove the ground and neutral in the panel and check for continuity.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Not sure about an AFCI, but a GFCI will trip if one of the devices is connected to a neutral wire for a different circuit.


Same thing. Cant mixmatch neutrals from different circuits, I guarantee if the OP takes the light fixture down he will find a pinched neutral.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Another question, do AFCI's have to be used for lighting cicuits in bedrooms or just mandatory for outlets?
I think the 2008 Code says "outlets", which in Code-speak means "any point on the wiring system at which current is taken to supply utilization equipment". This includes "receptacles" which is what I think you mean when you say "outlet". What we common folk call "lights" are really "luminaires". I'm sure anybody with a copy of the 2008 Code handy can confirm/deny this.
 

Jbfan74

Electrical Contractor
Messages
135
Reaction score
1
Points
18
Location
Newnan, GA
I think the 2008 Code says "outlets", which in Code-speak means "any point on the wiring system at which current is taken to supply utilization equipment". This includes "receptacles" which is what I think you mean when you say "outlet". What we common folk call "lights" are really "luminaires". I'm sure anybody with a copy of the 2008 Code handy can confirm/deny this.

It was mandated in the 05 code.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Right -- I knew there were AFCI changes in the 2008 Code, mistakenly thought the bedroom requirement had changed somewhat.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
What exactly was mandated, AFCI's on bedroom receptacles only? Any other places AFCI's are mandated? I am framing my new house currently and will be wiring soon, so this info will be handy.

Thanks,
Mark

Your gonna need alot more info than just AFCI requirements...
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
You should contact your local AHJ (inspector) ASAP and find out exactly what your local requirements are. They may be following the 2008 NEC, 2005, or a local conglomeration of NEC, local variations, etc. You could actually wire your new house strictly conforming to the 2008 NEC and fail a local inspection.
 

mc_1_2_3

New Member
Messages
23
Reaction score
0
Points
0
Location
Western Pennsylvania
This isn't the first house I have built, but it is the first one with the codes, (in Pennsylvania). I used to be an electrician, so the fundamentals haven't changed, just some of the requirements, like AFCI's. Couldn't buy them around here when I was an electrician. I have been in constant communication with the inspectors before I even designed the house, let alone start digging.

So, AFCI's in bedroom receptacles only, in general?

Thanks,
Mark
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Again, until the guys here know exactly what rules you're building under, they can't really give you the advice you're looking for. Your local inspector is the one to talk to. Also, depending on when you built that last house, you might be surprised to see how much what you consider "the fundamentals" have changed. If I may borrow from plumbing, there are only 2 fundamentals anymore, and only one of them is certain: electrons run uphill, and ******'s on Friday :D.

Now, why on earth did that word get censored?

As far as the specific issue of AFCIs goes, the 2005 Code requires AFCI protection on "all 120V, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms". Note the use of outlets, rather than receptacles. I think the 2008 Code requires them on all circuits in the house, with, of course, some exceptions.

If you've really been in constant communication with your inspector, you wouldn't be asking these questions here.
 
Last edited:

mc_1_2_3

New Member
Messages
23
Reaction score
0
Points
0
Location
Western Pennsylvania
Again, until the guys here know exactly what rules you're building under, they can't really give you the advice you're looking for. Your local inspector is the one to talk to. Also, depending on when you built that last house, you might be surprised to see how much what you consider "the fundamentals" have changed. If I may borrow from plumbing, there are only 2 fundamentals anymore, and only one of them is certain: electrons run uphill, and ******'s on Friday :D.

Now, why on earth did that word get censored?

As far as the specific issue of AFCIs goes, the 2005 Code requires AFCI protection on "all 120V, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms". Note the use of outlets, rather than receptacles. I think the 2008 Code requires them on all circuits in the house, with, of course, some exceptions.

If you've really been in constant communication with your inspector, you wouldn't be asking these questions here.

Yep I'm a liar. Sorry for asking questions on this forum. Guess that isn't what this is for, right? From now on I will direct all questions to the local inspector and ignore pricks like you.

Anyway, here is what PA code uses:


Building Codes
Search Printable Version Text-Only Full-Screen

UCC Codes

The UCC Administration and Enforcement regulation has adopted the following codes for use throughout the Commonwealth of Pennsylvania, effective 12/31/2006:
International Building Code 2006 (base code for commercial construction)
ICC Electrical Code 2006 (utilizes National Electric Code 2005 standards)
International Energy Conservation Code 2006
International Existing Building Code 2006
International Fire Code 2006
International Fuel Gas Code 2006
International Mechanical Code 2006
International Performance Code for Buildings and Facilities 2006 (provides alternative compliance approach)
International Plumbing Code 2006
International Residential Code 2006 (code for one- and two-family dwellings no more than 3 stories in height)
International Wildland-Urban Interface Code 2006

The codes currently in use under the UCC are the 2006 International Codes issued by the International Code Council. No supplements to the 2006 codes will be adopted for use. The next code changes will occur in 2009 (when the next triennial versions of the I-Codes are adopted by regulation).

Good day,
Mark
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
So, you'd prefer we tell you an answer that applied to a code your local inspector doesn't use and isn't applicable?

There is NO nationally applied, consistent electrical OR plumbing code, accepted in all locations. Some things are the same in any that apply, but many locales rewrite them to suit themselves. The ONLY way to be sure it meets local codes is to know exactly where you are, and which code they use.
 

Alternety

Like an engineer
Messages
768
Reaction score
0
Points
16
Location
Washington
As has been mentioned already above, check you fixtures. If neutral is touching ground the AFCI will trip. I found several Ikea ceiling lights with internally pinched neutrals that grounded. And one that grounded the hot wire. It was the luck of the draw which wire got pinched.

Test them disconnected before you put them up. And/or inspect visually. One of them was pinched but not completely through the insulation. Tightening it to the ceiling finished it.

The design was built in such a fashion as to almost require something getting the insulation pinched and grounded. They left wires running around that should have been tied down. And the final manufacturing or installation was done blindly so the problem could not be seen by the assembler/installer. Yes I reported it to Ikea.
 

Keith Wolf Ent

New Member
Messages
8
Reaction score
0
Points
0
Please Do not Pee Here

On each other over my question... I thank ALL of you for your advice, whether or not you agree with each other:) Let's all play nice:rolleyes:
 

KD

New Member
Messages
207
Reaction score
0
Points
0
The list of codes being followed is just a starting point. What matters is the local authority having jurisdiction (AHJ) interpretation of the codes. For example, one city near me says no AFCI protection on paddle fans or smoke detectors.
When I work in other AHJs, I have a check list that I go over with the inspector. This saves thousands of dollars.
 