Changing receptacle

Users who are viewing this thread

tlong_66

New Member
Messages
25
Reaction score
0
Points
0
I am changing one of the outlets in my kitchen. It is a kind i have never seen before where the wires push in from the back and are somehow locked in. Perhaps by a small metal tab on each side. Just wanted to check on proper way to remove so i don't damage anything.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
You're on target. Near where the wire is pushed in, there will be a small slot with a brass spring visible down in the slot. That spring digs into the wire to make the "back-stab" connection. Usually there's a stamped marking of "Press to release" or "Press spring thru slot to release wire" or something like that. With a small screwdriver, do just that -- press the brass spring, to move it away from the wire and it will release. Sometimes it's easier if you first push the wire in a bit to allow the spring to "un-dig" itself from the wire.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
1. Don't use that type again....they are notoriously unreliable , especially on a device which might have a toaster or coffe pot plugged in. Get the type where the wire goes straight in and is clamped when you tighten the screw.

2. If you do get the wire out of the old one, make sure there is no nick in it, which might cause it to break. You can't go wrong by cutting the old bare section off, and restripping.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
They are still legal for 15 amp circuits only. For many years, they have been required to exclude 12 gauge wire. I think that tells the story. Lots of folks use them because they are fast. In your own house, you get to choose.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
They are still legal for 15 amp circuits only. For many years, they have been required to exclude 12 gauge wire. I think that tells the story. Lots of folks use them because they are fast. In your own house, you get to choose.

I dont backstab just for the record, but I dont hold it against people that do either...
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
It's so well documented that backstabbing is failure prone it's not funny.
I am frankly surprised it is still legal.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
backstab01.jpg
 
Last edited by a moderator:

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
It's so well documented that backstabbing is failure prone it's not funny.
I am frankly surprised it is still legal.


Who did the documentation? and for what its worth Ive seen just as many bad splices as bad backstabbing, maybe we should not make splices legal either..
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
This is kind of like the plumbing arguments over AAV's and Sharkbites. They are code approved in many area. Folks have personal opinions about them, often based on personal experiences.

In all walks of life, professionals develop certain habits and preferences, and we will probably debate the issues forever. Putty or silicone??
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
My personal thoughts...

When used with a high current device, the spring pressure able to be exerted on the back-stabbed device decreases as the junction heats and cools. Eventually, it doesn't have as much pressure as when new. Then things start to get interesting. If used to just power a lamp or something, you may never notice, when used with say a toaster, you might. Better to use a screwed down clamp in my unprofessional view.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Please understand that this is not directed to anyone person but instead to the market in general.

Based on information that can be obtained from the CPSC and UL the installation of the stab-loc on 15 amp rated devices is as safe as any other type of installation.

It has been my experiences of over 40 plus years in the field and 8 plus in the classroom that most people don’t understand the failure of the device in the event one fails.

According to recorded statistics there are two reasons that the stab-loc fails. First and foremost is due to improper installations procedures and second is due to overload of the device. Failure due to overload will eventually end up with failure somewhere else in the device or circuit if not at the stab-loc.

Then we have the electrician or installer that just doesn’t know any better that just blames the failure on the installation procedure instead of the real problem. This is due to the lack of knowledge and a need to blame something in order to affirm their knowledge when this knowledge is absent. This is when we hear things like, “this guy is nothing but a hack or I would never do anything like this.â€

When I hear these types of statements I can’t help but wonder if the person making these statements thinks their knowledge and experience is far superior to those of Nationally Recognized Testing Laboratories which approves the procedure.

I also find that the electrician or installer that thinks that the stab-loc is a substandard installation are the same people that will spread the prongs of a male plug in order to get it to hold in a receptacle that is very loose. They don’t seem to understand that the receptacle that is loose is failing at the tension spring just as the stab-loc failed. They don’t understand that this loose receptacle is failing for the same reason that stab-loc fails. The loose receptacle is failing due to the device being overloaded.

A close study of Table 210.21(B)(2) will reveal to the reader that any 15 receptacle is to be loaded to a maximum of 12 amps no matter if it is installed on a 15 or 20 amp circuit. To connect a 1500 watt electric heater to this device for an extended amount of time will cause the device to fail. This failure will occur either in the blade slot or the stab-loc if used. Did the device fail due to the installation procedure of due to being overloaded?

Knowledge is power and power is the key to diagnosing a device failure. Without the proper knowledge one could simply make the statement that the electrician that made the installation was nothing but a money hungry hack and I am so much better than that hack.
Myself I prefer to have the knowledge to properly access the failure and give the customer the correct reason for the failure instead of trying to make myself look better than someone else with false information.
 

KD

New Member
Messages
207
Reaction score
0
Points
0
The best device connection is the screw and plate method found on recent GFCI receptacles and hospital grade receptacles. The around the screw is next, but its durability depends on the skill level of the electrician(or handyman). The stab-in or quick slot is worst. Here is the Question; What is the recommended torque for a receptacle screw?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
The best device connection is the screw and plate method found on recent GFCI receptacles and hospital grade receptacles. The around the screw is next, but its durability depends on the skill level of the electrician(or handyman). The stab-in or quick slot is worst. Here is the Question; What is the recommended torque for a receptacle screw?

I contend that if done propertly one is no better than the other.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Question; What is the recommended torque for a receptacle screw?
Leviton recommends 14-16 in-lb for their AC-215 and AC-220 duplex receptacles; hospital grade receptacles have a "designed torque capability" of 20 in-lb. Here's an abstract of a study intended to determine the effects of torque, contact area, and movement on the temperature of residential receptacles:

Testing was performed using 120 volt, 15-amp receptacles and copper wire to determine the effect of torque and wire contact area on temperature elevation at receptacle screw terminals. Torque was varied on both the hot and neutral terminals from 0 to 12 in-Ibs, and the apparent wire contact at the screw terminal was varied by 1/8" and 5/8". There was no significant difference in temperature when changing apparent wire contact. Increased temperatures were observed with reduced torque, however, they were not significant enough to initiate a glowing connection, nor high enough to cause rapid oxidation. Further testing showed that movement of a loose connection was necessary to cause significantly high temperature changes, arcing and sparking, rapid oxidation, and in some cases, glowing connections.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Please understand that this is not directed to anyone person but instead to the market in general.

Based on information that can be obtained from the CPSC and UL the installation of the stab-loc on 15 amp rated devices is as safe as any other type of installation.

It has been my experiences of over 40 plus years in the field and 8 plus in the classroom that most people don’t understand the failure of the device in the event one fails.

According to recorded statistics there are two reasons that the stab-loc fails. First and foremost is due to improper installations procedures and second is due to overload of the device. Failure due to overload will eventually end up with failure somewhere else in the device or circuit if not at the stab-loc.

Then we have the electrician or installer that just doesn’t know any better that just blames the failure on the installation procedure instead of the real problem. This is due to the lack of knowledge and a need to blame something in order to affirm their knowledge when this knowledge is absent. This is when we hear things like, “this guy is nothing but a hack or I would never do anything like this.â€

When I hear these types of statements I can’t help but wonder if the person making these statements thinks their knowledge and experience is far superior to those of Nationally Recognized Testing Laboratories which approves the procedure.

I also find that the electrician or installer that thinks that the stab-loc is a substandard installation are the same people that will spread the prongs of a male plug in order to get it to hold in a receptacle that is very loose. They don’t seem to understand that the receptacle that is loose is failing at the tension spring just as the stab-loc failed. They don’t understand that this loose receptacle is failing for the same reason that stab-loc fails. The loose receptacle is failing due to the device being overloaded.

A close study of Table 210.21(B)(2) will reveal to the reader that any 15 receptacle is to be loaded to a maximum of 12 amps no matter if it is installed on a 15 or 20 amp circuit. To connect a 1500 watt electric heater to this device for an extended amount of time will cause the device to fail. This failure will occur either in the blade slot or the stab-loc if used. Did the device fail due to the installation procedure of due to being overloaded?

Knowledge is power and power is the key to diagnosing a device failure. Without the proper knowledge one could simply make the statement that the electrician that made the installation was nothing but a money hungry hack and I am so much better than that hack.
Myself I prefer to have the knowledge to properly access the failure and give the customer the correct reason for the failure instead of trying to make myself look better than someone else with false information.

Can't disagree with anything you say. On the other hand, it seems that in the real world, J.Q. Public WILL find a way to tax a 15 amp receptacle beyond its means....with extension cords to multitply hair dryers and coffee pots.

If your experience has been that you have not replaced a lot of receptacles where the back-stab connection failed, then that is the experience, and as I mentioned, we all expect professionals to learn from their experience and act accordingly.
 