Yet another vent question....(sketch)

Users who are viewing this thread

SuperDaddy

New Member
Messages
24
Reaction score
0
Points
0
Location
New York
Just wondering if it is possible to vent a toilet in this manner (see pic).

4" waste with a 3" vent line coming off the back of the waste line.

I'm not sure if this is acceptable or not. I am worried about the actual "waste" getting caught on the tee portion on the "way down".

I searched, but couldn't find anything that dealt with this scenario.

Any thoughts?


29417987zq8.jpg
 

Basement_Lurker

One who lurks
Messages
664
Reaction score
1
Points
0
Location
Victoria, BC
Why don't you have the tee under the wall instead of the toilet and have a 90 going from under the toilet into the branch connection?

Otherwise, if you are determined to use your current setup, you can swap out the tee for a wye fitting.
 

BAPlumber

Plumber
Messages
227
Reaction score
2
Points
0
Location
Vashon, Washington
this is a fairly common setup for older homes. the (barrell vent) usually is used with a 2" Vent (code), I've seen it with a 3/4" vent (not code). I don't see a problem with a 3" vent, but no advantages.
 

Bombjay

New Member
Messages
62
Reaction score
1
Points
0
dothisie8.th.jpg


Hope this quick scribble helps.It shows a 4x3 toilet bend into a sanitary tee that is below your 3" vent
 